Hi.

Does anyone here know how to calculate approximately how much power an
online/double-converting/sine wave UPS consumes from the mains? I guess
that, if it has to keep N 12V batteries charged, the most power it can
consume is (a bit higher than, depending on efficiency) N*12V*c, where
c is the maximum charging current. Am I missing anything?

(For my 1KVA online UPS, which has 3 65AH/12V batteries and charges them
at up to 6A, I speculate that the maximum power used is 6*3*12=216W, and
when the charger is "floating" to keep the batteries charged, the power
use is pretty much negligible.)

Second, can anyone comment on the advisability of charging SLA (sealed
lead acid) batteries at currents of >=0.1C (i.e. 10% of their rated Ah
capacity or more)? My UPS vendor says they've had problems with current
that high, and the battery FAQ says <0.1C for SLAs, but battery vendors
seem to recommend 10-20% even for SLAs. Does this differ significantly
for VRLA batteries?

Third, can anyone explain in detail the internals of a constant-voltage
battery charger? I understand the basic idea: provide as much current as
needed to maintain the voltage across the terminals at the recommended
charging level, but I don't understand enough about how batteries work
to figure out what happens when you apply a higher current, or how the
voltage is measured or maintained.

Also, does anyone know how much I should expect to spend on a basic DC
ammeter (the nifty clamp-on hall effect ones, not an in-circuit one),
preferably in India?