Scott, you are absolutely correct, and shutting down the fan, if
anything, makes the obstruction problem worse if the blade stops in the
wrong place (which, according to Murphy's law, it will).
As regards the testing done by the manufacturer, unless it was
full-scale fire testing or ADD testing, it will tell you nothing obout
the effece of the obstruction.
Joe
Scott A. Futrell wrote:
Since fire alarm systems are not desired or required in most of these
storage occupancies, the only fire alarm system that will shut down the
fans is the operation of the water flow switch on the sprinkler systems
and if that is delayed because of the fans, I fail to see how that helps
the situation, or should be allowed.
Scott
(763) 425-1001 Office
(612) 759-5556 Cell
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of hughes
rewis
Sent: Tuesday, November 28, 2006 7:14 AM
To: [email protected]
Subject: Big Ass Fans
Well, I dug a little deeper into my filing system and found the
documents
sent to me from the manufacturer. In it ESFR sprinklers are discussed.
In
capsulated form it states that the two issues are obstruction and air
velocity. First it says that the fans are shut down when the fire alarm
system responds to a fire situation. Air velocity is typically limited
to 5
ft/sec. It goes into great detail of test in several diffent senarios,
of
which I will not go into. Quite lenghty.
Though I'd pass this along.
Thanks,
Hughes
_________________________________________________________________
Stay up-to-date with your friends through the Windows Live Spaces
friends
list.
http://clk.atdmt.com/MSN/go/msnnkwsp0070000001msn/direct/01/?href=http:/
/spaces.live.com/spacesapi.aspx?wx_action=create&wx_url=/friends.aspx&mk
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum