Roland please ignore the request for the old allowances, I believe I have
them satisfied that they are 8.14.7.2, 8.14.7.3 and 8.14.7.4. 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Kathy Blair
Sent: Thursday, November 30, 2006 8:14 AM
To: [email protected]
Subject: RE: Limited-Combustible Material and exterior canopies

Thank you very much for your reply and also for looking into addresses this
with the committee for the 2007 edition.  However, you keep mentioning the
three old allowances and the AHJ is asking for those to be called out.  So I
hate to ask but could you please list those three allowances?
Thank you Roland,
Kathy  

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Wednesday, November 29, 2006 5:13 PM
To: [email protected]
Subject: Re: Limited-Combustible Material and exterior canopies

This is actually an excellent nuance that merits closer review.   
Unfortunately, the problem with learning something NEW is that it typically
displaces some older bit of knowledge- lol.

The use of limited or non-combustible varies slightly but significantly
depending on which portion of the canopy we are evaluating.  Actually we
have to look at the canopy from THREE aspects.  First off, we must look at
combustibility of the entire assembly.  8.14.7.2 says sprinklers omitted
where the canopy is of  
non or limited combustible construction.   For this aspect of the  
canopy, the general definitions from chap 3 apply.  This is when it is NOT
just the exposed surfaces but includes evaluating a cross sectional or
longitudinal  cut of the assembly.  So if the entire assembly is non or
limited combustible construction, sprinklers can be omitted from both UNDER
(assuming no storage beneath it) and WITHIN  the canopy.  I state the
obvious because I just saw a disconnect within the linked criteria.

So we have combustible construction and must look at what is be protected
and how limited combustible is applied.  For the inner portion STOP THINKING
CANOPY and think CONCEALED COMBUSTIBLE SPACE.  
Now whether or not the 4 ft wide trigger from 8.14.7.1 applies, can  
be argued. After all, it does say UNDER the canopy is not required.    
Nonetheless, lets shift to 8.14.1.1 which says  "spaces enclosed wholly or
partly by EXPOSED combustible construction.  SO with a combustible assembly
with non or limited combustible exposed surfaces (as defined within 8.14.1.2
allowances), no protection is required within the concealed space.

Now lets look at UNDER the canopy.  New criteria from 07 says a combustible
canopy WITH NON OR LIMITED COMBUSTIBLE EXPOSED SURFACES BENEATH with either
sprinklers within the concealed space or the three old allowances (and no
storage beneath), sprinklers can be omitted FROM UNDER THE CANOPY.  This is
where we disconnect from the linked criteria.  Even if 8.14.1 allows no
sprinklers in the concealed space (unless its the same allowances as in
8.15.7.3 of the 07b ed), we would have to sprinkler UNDER the canopy for a
combustible assembly with no exposed combustibles construction if we elect
to omit them.

I don't think the committee looked at this variant and am glad just to see
the allowance for omitting sprinklers when the concealed portion is
protected.  I have put this on my list of things to explore for the next
cycle.

Roland

On Nov 29, 2006, at 1:31 PM, Kathy Blair wrote:

> I have the same question, with the following situation:
> 2 x 8 wood  joists with stucco tight to the bottom of the joists and 
> stucco on the building and columns and the ceiling is at 20'-0" in 
> height, it is
> only a pedestrian walkway.  The code being used is 2002 Edition.   
> The fire
> department or AHJ is requesting for me to add pendents because of the 
> combustible construction located within.
> May I have some advice on if they are required and maybe some 
> arguments for not installing them just because it is required and from 
> what Roland stated that the 2007 Edition would not require them.  At 
> least I believe that is what Roland was saying, my apologizes if I was 
> not correct.
> Thank you in advance,
> Kathy
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Randy 
> Knutson
> Sent: Wednesday, November 29, 2006 12:39 PM
> To: [email protected]
> Subject: Limited-Combustible Material and exterior canopies
>
> Would an exterior canopy made from composite wood joists sandwiched 
> between a steel roof and sheetrock be considered limited-combustible 
> construction?
> I'm wondering if I could omit sprinklers under an exterior canopy per 
> 8.14.7.1.
>
> I'm hung up on the limited-combustible construction definition.
>
>
>
> Thanks,
>
>
>
> Randy Knutson
>
> Shilo Automatic Sprinkler, Inc.
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to