Richard:

To clarify terminology, what I was trying to describe with the term 
"essentially performance-engineer" is the methodology for the basis of the 
design, not to literally promote performance-based design which is a different 
exercise altogether and having to do with alternative means and methods of 
compliance with codes and standards.   What I proposed in committee and what I 
am saying still is that the design should be matched to the performance of the 
equipment carried by the responding fire department.

There are still straight stream nozzles in use by fire departments and there 
are likely some that use 2" or 2-1/2" inside of buildings.   But the VAST 
majority of fire departments use 1-1/2" or 1-3/4" hose packs, and many pull 
them from gated wyes as Rich and I both described.  (Over the course of the 
last 3+ year cycle we had 4 days of task groups and took a lot of comments and 
correspondence from fire service - this is not just my opinion.)  How do we 
guarantee that they keep using the same gear?   We can't.  So wouldn't it be 
prudent to promote designs that are conservative enough to work reasonably well 
across-the-board?   It can't be said that 100 PSI is adequate for most or many 
or maybe even half of the departments out there who are rigged for response to 
mid-rise and high-rise fires. 

Would you agree that 75 PSI at the riser base will serve most sprinkler 
systems?   Why don't we just require 75 PSI, go back to pipe schedules and 
leave it at that?   What I proposed was pretty straightforward and did not 
include flow modification; it was to require that the discharge pressure be 
adequate to deliver the required pressure at the nozzle tip(s), based on the 
actual equipment used.  A recommendation to designers and fire service has been 
in the standard for at least 3 or 4 cycles (A.7.8 in 2003 and 2007), that the 
required nozzle pressure and actual set-up should be considered.  I agree with 
your statement that many cities - small, medium and large - may not know how 
their equipment performs or what pressures are needed.  So we should look the 
other way?  Are you saying that's just a fact of life and it's okay to send 
firefighters into a building with gear that may not perform at it's optimum 
level?   There is no excuse for ignorance and oversight if the information is, 
in fact, readily available to us.

It is incumbent upon fire brigades to train their personnel in the equipment 
and tactics they have adopted, and the administration of those departments has 
a responsibility to maintain continuity within reason.  That's one of the 
benefits of having a wide range of nozzles available - some FD's carry 
different rated nozzles on their trucks to assure as much as possible that 
they'll get the best match for the fire and building in which they're working.  
 And we as an industry can accommodate whatever they want.  But unlike 
sprinklers (or just about any other building system), the end-user of a 
standpipe system is the fire department.  They should have some ownership of 
the design and I stand by my statement that the design development sequence 
should begin with contacting the responding FD.

Steve Leyton
Protection Design & Consulting

The foregoing is the opinion of the writer alone, and does not necessarily 
represent the intent of the NFPA 14 Technical Committee, nor constitute a 
formal or informal interpretation of the standard.







-----Original Message-----
From: Richard Malek [mailto:[EMAIL PROTECTED]
Sent: Wednesday, December 06, 2006 6:22 PM
To: [email protected]
Subject: RE: pump capacity/standpipe


Steve,
It is good to see you are thinking outside the box some, but I'm somewhat
glad your performance-based approach to standpipe design was voted down. The
comments that Chris makes regarding FD's have quite a bit of truth to them.
You can design for what the SDFD or what any FD wants today, however, as
Chris points out, that can change with a new fire chief or fire service
changes in strategy/tactics or just pure fads. That building and standpipe
however is going to be there for many decades. Over those many decades, how
many different performance-based designs are there going to be in just one
city? And those are on top of the 100 psi and 65 psi designs and even
earlier crtieria.

Did your performance-based proposal also allow modifying the flow per outlet
as well? Unless an FD is using 2 1/2" or maybe 2", they are not going to
flow 250 gpm at a reasonable outlet pressure. If they are going to use 1 1/2
or 1 3/4" hose, the max gpm is probably only in the 175 gpm range. If we are
going to force owners to pay for the extra pressure, why make them pay for
gpm the FD will not use?

There are a number of options out there to make good use of the current 100
psi outlet pressure. Every dept still has the option of 2 1/2" and many use
it. For those that don't want to lug the bigger hose, a 2" line is
well-sized for standpipe use. 2" line with a smooth-bore could deliver in
the 225 gpm range and isn't much more difficult to handle than an 1 3/4".

You portray somewhat the best case scenario with FDs that know how they want
the standpipe to perform, Unfortunately, many small and mid-size cities, and
probably even some bigger ones, aren't in that position and there is a lot
to be said for standardization and where over time there is knowledge
building on the fire service side and where neighboring (or not so
neighboring in the internet world) can learn from each other how to properly
utilize a "standard" design standpipe. I think this is an area where
industry can assist FDs in understanding the design and how to match
equipment to it vs. throwing key design criteria over the fence to the FD
and asking  "tell us what you want."

Interesting discussion.

Rich

Richard Malek