Have you ever gone to test an anti-freeze system, and wondered what they put
in it? Glycerin? Glycol?
Was the piping steel, copper or CPVC?
We have run into this a lot lately. The only simple test I know of is from
the Noble company, called "No-Burst test strips" They created this product
for their No-Burst Glycol radian heat product, but it has a very useful
application for fire sprinkler contractors doing testing and inspections.
The strips will react (Change color) if there is any type of Glycol in the
system sample. Either Propylene or Ethylene Glycol. It will not react if
there is Glycerin in the sample. While it would be nice if it would say turn
red for Glycol and blue for Glycerin, it doesn't. We still find this a very
cheep and useful tool, and one all service and inspection personnel should
carry to work on any anti-freeze system.
(Noble is the MFG of Firefighter PG and GL, and should be available from
your usual suppliers.)
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message -----
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum