In the event of a conflict between a code and a standard, we have always allowed the code to be the requirement. For examply the IBC requires a 2 hour duration for the emergency generator for high rise buildings, but the IFC requires the emergency generator to be installed in accordance with NFPA 110 and 111. The NFPA standard has a duration far in excess of 2 hours, but the project only has to meet the 2 hour requirement.
WHat is the exact conflict you are involved with? Rich Richardson Seattle FIre Department >>> Todd Williams - work <[EMAIL PROTECTED]> 01/02/07 9:30 AM >>> Say an NFPA standard is adopted as part of a building code. The building code allows a modification of the NFPA standard. Do the building code and NFPA standard then become conflicting codes and the more stringent apply? Todd G. Williams, PE Fire Protection Design/Consulting Stonington, Connecticut 860-535-2080 www.fpdc.com _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum