NFPA 13 does not stipulate a maximum limit on velocities; some insurances
companies modify NFPA 13, such as FM, to restrict 20fps on gridded sprinkler
systems.  I believe NFPA 15 does require velocities pressures.  Anyway, I
was always taught that good engineering practices restrict velocities
pressures to a maximum of 32 fps in branchline piping.  

Hope this helps.
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ivan Cabrera
Sent: Tuesday, January 09, 2007 4:58 PM
To: [email protected]
Subject: max velocity

Would anyone be able to give me any info on the max velocity for
sprinkler piping? If so, can you give me a code section it would be
under?

 

Thank you,

 

Ivan Cabrera