Tennessee where I work requires licensing. 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Chris Brown
Sent: Wednesday, January 10, 2007 3:52 PM
To: [email protected]
Subject: RE: Testing

But when you look at the number of states that have a license requirement
they are few. There are many of the larger cities have requirements but not
as a state. Look at Oklahoma, They have one of the best licensing
requirements I am aware of and they enforce it well for both the fire alarm
and fire sprinkler industries. I think every state should be looking at what
the State of Oklahoma is requiring. Look at the web site for Oklahoma
Department of Health of the requirements if interested. They are doing the
right thing! Every one associated with fire protection has to be licensed.


Thank you,

Chris Brown
Fire Protection Designer, Poole Fire Protection
Office: 913.829.8650   Direct: 913.747.2056   Cell: 913.208.3600   Fax:
913.829.8690


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: Wednesday, January 10, 2007 2:37 PM
To: [email protected]
Subject: Re: Testing

there is a fine point you are missing.  The OWNER of a PRIVATE facility is
typically allowed to do as much of their own work  as they want to.
It's when you hire out to do work for someone else that licensing enters the
equation.

Roland

On Jan 10, 2007, at 12:29 PM, <[EMAIL PROTECTED]> wrote:

> Chris, Kansas isn't alone on that.  I have a project in a nearby 
> state.
> The owner wanted to do the installation himself.  He has mechanics 
> that know how to use a pipe wrench.  (this guy wanted a detail on his 
> drawings of how to install an upright head, yes we are in
> trouble.......)
>
> Anyway, when I called the state board of licensure and asked the lady 
> if you had to be specifically licensed to install sprinkler systems 
> her words were, "that's a good question, I don't know",  so she passed

> me off to her department manager, who obviously read from the same 
> script
> because he said the same thing.   Seems in their state and local
> municipality don't require permits or system inspections and so anyone

> can install it.
>
> There is no consistency in the laws concerning licensing.
>
> Craig L. Prahl, CET
> Fire Protection Group
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC  29304-0491 Direct - 864.599.4102 Fax -
> 864.599.8439 [EMAIL PROTECTED] http://www.lg.com
>
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Chris 
> Brown
> Sent: Wednesday, January 10, 2007 3:17 PM
> To: [email protected]
> Subject: RE: Testing
>
> In the state of Kansas all you need is transportation to the site it 
> even could be by mass transit and you can work on any type of fire 
> protection system. Wichita has some requirements and Kansas City 
> Missouri has a sprinkler contractors license requirement but other 
> than that any one can work on any fire protection system. We have 
> plumbers installing sprinkler systems and electricians installing fire

> alarm system. They don't even know what NFPA is.
>
>
> Thank you,
>
> Chris Brown
> Fire Protection Designer, Poole Fire Protection
> Office: 913.829.8650   Direct: 913.747.2056   Cell: 913.208.3600    
> Fax:
> 913.829.8690
>
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Gregg 
> Fontes
> Sent: Wednesday, January 10, 2007 1:56 PM
> To: [email protected]
> Subject: Testing
>
> Does a C-10 and/or electrical/alarm contractors license allow them to 
> contract the testing of water base fire protection systems?  (I.E.
> opening inspectors test valves, operating control valves, testing of 
> Pre-action/Deluge/Dry systems, generally can they operate any 
> component of a fire sprinkler system that has an alarm affiliated with

> it?)
>
> Gregg Fontes
> Cen-Cal Fire Systems, Inc.
> 209-334-9119
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to