Here is a good example why we don't run fire supply mains under building slabs. 
NFPA has prohibited this for years but I still Architects and Engineers design 
underground fire supply mains under the slab to interior mechanical rooms. Fire 
sprinkler risers should always be installed at exterior walls to prevent what 
just happened at Sky View High School. Please pass this along to anyone in your 
firm who specifics location of fire supply mains.

NFPA 13 2002
10.6 Protection Against Damage
10.6.1 Pipe shall not be run under buildings.
Piping located under buildings is extremely difficult to repair, which is one 
of the reasons that
10.6.1 prohibits the installation of pipe under buildings. When buildings are 
built over exist- ing underground piping, the piping should be rerouted around 
the new building. When piping buildings requires repair, operations in the 
building must be curtailed, equipment may need to be moved, and the floor must 
be excavated. Leaks in the buried piping underneath the building can go 
undetected for long periods, and they can also undermine the building support.
The location of system valves in the center of a building also places the 
system controls in the center of the building, which may not be desirable 
during a fire event.

http://www.billingsgazette.net/articles/2007/01/11/news/local/25-skyview_g.t
xt




Joe Burtell, SET, CFPS
Burtell Fire Protection, Inc.
[EMAIL PROTECTED]
www.burtellfire.com
 


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to