Anyone have any data if you space the heads at 7'6" will it work?? Does 6" matter that much??? I have heard FM can/have relaxed the 1' rule to 6" on obstructions on existing installation, which this is, anyone confirm? If we move the heads more then 1' foot then we just move the obstruction to the next head. How about a draft curtain?

Thanks

Tom


From: Joe Hankins <[EMAIL PROTECTED]>
Reply-To: [email protected]
To: [email protected]
Subject: Re: ESFR On Line Spacing Less Then 8' Options??
Date: Sun, 14 Jan 2007 20:45:23 -0500

Tom,

Baffles won't help you. The problem with close spacing is that water droplets from a sprinkler operating over a fire are carried upward by the fire plume, cooling adjacent sprinklers and resulting in skipping, regardless of the presence of baffles. Water spraying directly from one sprinkler to the next is not the issue.

Joe

Tom L wrote:

I have a client with ESFR system obstructions and I am looking for options.

Here is what I have, the heads are K17 pendent with 23 lines running East to West. One head on each line is obstructed in the same location by being too close to bar joist. If we move the head so it is 12" from the obstruction it will be 7'6" away from the adjacent sprinkler, less then the 8' required by NFPA and FM 2-2. I can not use an upright K 17 because I have exposed non-expanded plastics.

Only option I can think of is to install a baffle on the 23 heads to prevent the water from one ESFR hitting the other. Any idea how large this baffle should be? I am thinking 2' wide by 2' deep with the ESFR head centered. The heads are 10-14" below the desk.

Suggestions comments?

Thanks

Tom LaCorte
Chubb Insurance Co

_________________________________________________________________
Type your favorite song. Get a customized station. Try MSN Radio powered by Pandora. http://radio.msn.com/?icid=T002MSN03A07001

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_________________________________________________________________
Fixing up the home? Live Search can help http://imagine-windowslive.com/search/kits/default.aspx?kit=improve&locale=en-US&source=hmemailtaglinenov06&FORM=WLMTAG

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to