Paul,

If you are advocating adding reality of D-W formula (or H-W) and a supply
calc why not go one step further and add reality of the number of heads that
will operate.  I would contend if all operate the fire will cause a total
loss to the building and the size of the containment should be ridiculously
large like 100 times the sprinkler demands, H-W in RA times time and be
outside the building.  Either a hand full of heads control the fire or
master streams come out.  That's maybe an exaggeration but small at best.  I
can probably count on one hand the number of times the exact number of heads
calculated operates and the building didn't burn down. 

Hose demands?  That's different! Also when the hose streams come out the
supply calc goes down.  

Want to get really fancy consider the ADD.  How much will evaporate before
it gets to containment and how much goes back up in the plume?  

I think just keep it simple unless you have failures. 

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [EMAIL PROTECTED]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Paul
Sincaglia
Sent: Tuesday, January 16, 2007 7:51 AM
To: [email protected]
Subject: RE: NFPA 30 (03ed) - curbs

How would you determine the "expected discharge" from the sprinkler
system. 
Dewayne 


Ahhhh...the loaded question!!  

First, I have to say you should check your local codes.  The IFC
requires spill control to handle the largest spill plus 20 minutes of
suppression water.  However, if you have other performance goals you may
need to alter this...but keep in mind that the local code will be your
minimum.

Now, the fun part and the point that will no doubt spawn debate all day.
How do you determine the amount of water you need to retain?

I've seen two schools of thought with lots of modifications.

The first, simplest, and probably the most common method to do this is
to perform your normal hydraulic calculations and simply take the total
flow rate produced by the design basis and multiply by the code's 20
minutes.  This gives you a volume figure (gallons) and then you size the
curbs around the containment area to hold it.  Some people include the
hose stream allowance, some don't....I say you should include it.

However, one always needs to remember that our normal means of doing
hydraulic calculations does not calculate actual output.  So if you use
the calculation method above, you are likely only providing 10-15
minutes of containment.  Which brings me to the better
alternatives...provided your calculation software has the capability and
you have accurate water data.

Most hydraulic programs can do what is called a supply calculation.  It
essentially performs a hydraulic calculation that has no safety factor.
i.e. what will the water supply actually push though the pipes if the
entire coverage area is flowing.  Generally speaking this flow rate is
15-20% higher than your demand calc, but can really be all over the
place depending upon your water supply and your base sprinkler design.

Now, I generally like this method as it makes a lot of sense to people
when you explain how you got your answers.  However, as the forum has
been kicking about for days now...Hazen-Williams overestimates friction
losses at higher pipe velocities.  For our normal demand calculations
this is no big deal as it provides an additional level of safety in our
designs.  But in the supply mode, particularly at higher velocities, the
fiction loss is overestimated, therefore the water discharge gets
underestimated as the flow gets artificially choked by the friction
inherent in the Hazen-Williams method.  

For what it is worth, I personally don't think that the errors in the
supply calculation using Hazen-Williams is all that big a deal.
However, I have never done any studies or seen any data to support that.
I just know that my figures are still slightly lower than what the
actual output will likely be IF the entire coverage area where to
activate AND the water supply remains the same.

So that is how I would handle it...Using the supply calculation method.
But I am sure that many others have many other opinions.  So let the
games begin.  

So that I can salt the wound a bit....If you are the code consultant,
how do you estimate the containment required when no one has even
started the sprinkler designs yet?  I have my method...What is yours?

Now for real work...


Paul Sincaglia, P.E.
President
Firesafety-Solutions, Inc.
440.247.3770

 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Tom L
Sent: Monday, January 15, 2007 6:40 PM
To: [email protected]
Subject: RE: NFPA 30 (03ed) - curbs

Dewayne,


So do you have a foam system or not? If you do then curbs without
drainage is OK If you have a water only system then u will need drainage
with the curbs.

Review figure 6.8.5 on page 57 of NFPA 30, 2003 edition, it will
indicate IF you need to provide spill containment OR liquid spread
control. Curbs are used if you have a closed head foam system to control
the spread of the product mixed with the water (section 6.4.2.5). If you
have a water only sprinkler system and you have a Class I-IIIA liquid
then, you need to provide liquid spread control as per 6.8.5.1.


Take a look at FM data sheet 7-29 it has more up to date sprinkler
protection requirements then NFPA 30/ 2003 edition.

Regards

Tom

Chubb Insurance

>From: "Dewayne Martinez" <[EMAIL PROTECTED]>
>Reply-To: [email protected]
>To: "SprinklerFORUM" <[email protected]>
>Subject: NFPA 30 (03ed) - curbs
>Date: Mon, 15 Jan 2007 10:51:03 -0600
>
>Section 6.4.2.5 deals with curbs, scuppers, special drains, ect....and 
>states that "If a drainage system is used, it shall have sufficient 
>capacity to carry the expected discharge of water from the fire 
>protection systems and hose streams."
>If there is only curbs does this apply since there is technically no 
>drains?  If so, what is the proper way to determine the expected 
>discharge?
>Thanks,
>Dewayne
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_________________________________________________________________
Type your favorite song.  Get a customized station.  Try MSN Radio
powered by Pandora. http://radio.msn.com/?icid=T002MSN03A07001

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to