Tom,

The only difference from pendants as regards obstructions is that single obstructions up yo 4 in. wide can be ignored with uprights. It's application is much more limited than pendants, e.g. it has a 35 ft. building height limitation and can only be used to protect cartoned unexpanded plastic.

Joe

Tom L wrote:

Joe,

What is the obstruction criteria for an upright ESFR? FM 2-2 and NFPA13 is not clear. Can you provide some guidance or point me to a code section I have missed? I know is it less then the pendent ESFR but what to you follow? I have been told it has the same criteria as a standard head , is this correct?

Thanks

Tom


From: Joe Hankins <[EMAIL PROTECTED]>
Reply-To: [email protected]
To: [email protected]
Subject: Re: Mismatch of upright and pendent sprinklers
Date: Thu, 25 Jan 2007 21:27:15 -0500

Dan,

That is almost exactly what was tested. The concern was that the upright would operate first and prevent the pendant from operating. It operated first, but the pendant operated almost immediately after it. It makes a good solution for obstruction problems in existing systems, but the 35 ft. height limitation can be a deal killer.

Joe

Dan Arbel wrote:

If there is no problem of mismatch,

Then what about the difference in clearance between the two types.

In one particular case I found the upright at 5in and the pendent at 14in
clearance, next to each other.

Dan

Dan Arbel Risk Eng
T:  +972 (04) 8243337
F:  +972 (04) 8243278
M: +972 (052) 2810593


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Roland
Huggins
Sent: ä 25 éðåàø 2007 21:39
To: [email protected]
Subject: Re: Mismatch of upright and pendent sprinklers

No restrictions that I am aware of.

If memory serves me right, FM made an earlier statement that localized upright ESFR sprinklers could be used within an otherwise pendent ESFR system. That had to break the heart of the mfg that developed the first upright (since they are far superior in regard to obstructions).

Joe - any comments?

Roland

On Jan 25, 2007, at 9:31 AM, Dan Arbel wrote:



Dear All,

What is your opinion regarding the use of upright and pendent ESFR
sprinklers in the same area?

What about mixing brands of different manufacturers?

Dan





Dan Arbel Risk Eng
T:  +972 (04) 8243337
F:  +972 (04) 8243278
M: +972 (052) 2810593



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum




_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum




_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_________________________________________________________________
Check out all that glitters with the MSN Entertainment Guide to the Academy Awards® http://movies.msn.com/movies/oscars2007/?icid=ncoscartagline2

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to