The definition os a Clas III requires 1½" Hose statoins (hose included) and 2½" 
hose connections;

3.3.27.3 Class III System. A Class III standpipe system provides
38-mm (11⁄2-in.) hose stations to supply water for use by
building occupants and 65-mm (21⁄2-in.) hose connections to
supply a larger volume of water for use by fire departments
and those trained in handling heavy fire streams.

-----Original Message-----
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams - 
work
Sent: Tuesday, January 30, 2007 2:12 PM
To: [email protected]
Subject: RE: NFPA #14 and pressures


And even if they find one, would you trust an 
untrained person on the end of a hose with 100 psi discharge?

At 03:02 PM 1/30/2007, you wrote:
>One thing that does not make sense....where are
>these untrained people going to get 1 1/2" hose?
>
>Paul J. Pinigis, P.E.
>Chief Life Safety Engineer
>
>
>
>Must meet both criteria. The 1½" hose station is available for 
>untrained persons thus the pressure limit.
>

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com 

_______________________________________________
Sprinklerforum mailing list
[email protected] 
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to