So I take it that you have never installed ESFR sprinklers in a building
that included roof drains that run from the roof deck to the floor along
a column?     

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Joe
Hankins
Sent: Wednesday, February 07, 2007 7:51 AM
To: [email protected]
Subject: Re: ESFR AND VERTICAL OBSTRUCTIONS (NFPA 13 07ed)

Dewayne,

If it is impractical, then don't install ESFR's. There are other
alternatives (e.g. in-rack sprinklers).  ESFRs are an option only if
their installation rules are met.

ESFR's are asked to do a lot more than any other sprinkler. As a result,
there is no margin for error when it comes to obstructions.  If there is
a single obstruction and the fire starts in the wrong spot, then failure
to suppress or control is a very real possibility. 

In the testing of ESFR sprinklers, the scenario of a fire starting
centered between two sprinklers with one of them obstructed resulted in
a barely controlled fire in a 30 ft. building (11 sprinklers operated)
and uncontrolled fire in a 40 ft. building.

Joe

Dewayne Martinez wrote:

>I am looking for some input from the forum on how you treat  a isolated

>vertical obstruction that restricts only one ESFR sprinkler head.  It 
>is both above and below the sprinkler.  Such as a round exhaust duct 
>from a unit heater below up through the deck or a plumber drain stack?

>An informal request to NFPA resulted in this response "Section 
>8.12.5.2(5) allows sprinklers with special obstruction allowance shall 
>be installed in accordance with its listing. ESFR sprinklers have very 
>particular obstruction criteria, and interpolation, or modification of 
>obstruction rules is not allowed."  I have yet to find a ESFR sprinkler

>to address this issue, in the past I have followed the rules for 
>isolated obstructions below the sprinkler to provide guidance.  It 
>seems impractical to expect a storage building to be constructed 
>without any vertical obstructions.
> 
>Thanks,
>Dewayne Martinez
>Design Build Fire Protection
>[EMAIL PROTECTED]
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>  
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to