Thanks Ed. I have a copy and see that it is under Hose Allowance,
which I would have glossed over in context with a tank. The room in
question is 496 sf so the idea to divide the room surfaced until
reading the "with no such rooms adjacent" clause.
Allan Seidel
St. Louis, MO
On Feb 9, 2007, at 12:07 AM, Ed Kramer wrote:
Allan,
If you have a copy of the 2007 flavor of NFPA 13, look at the new
section
11.1.5.2 (3). As long as the higher hazard areas are enclosed & no
greater
than 400 sf and separated from other higher hazard areas, you're
allowed to
use the duration and hose allowance for the lower hazard. Nice
addition.
Ed Kramer
Littleton, CO