The NEC doesn't allow life safety systems to operate of a gas fired
generator. You need local AHJ approval to use them.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message -----
From: <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Friday, February 16, 2007 8:35 AM
Subject: RE: back-up power
Why propane versus the more common and probably cheaper diesel?
Environmental issues, i.e. exhaust?
Is your primary power source considered non-reliable thus necessitating
a secondary backup source?
Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC 29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams - work
Sent: Friday, February 16, 2007 9:39 AM
To: [email protected]
Subject: back-up power
I am working on a project where an electric fire pump (diesel not an
option) and tank is the only source of water for the sprinkler system.
The primary supply is the public utility and the back-up is to come from
an on-site generator. The builder is proposing to use a propane-fired
generator. I looked in NFPA 20 and 110 and didn't see anything saying
this was a no-no. Is there a problem with this arrangement?
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum