Joe,

Not that it is a perfect argument, but I have argued that the 2006 edition
of IBC allows a manual standpipe and requested a variance in the past.



2003 EDITION

*905.3..4 Exception: Where the building or area is equipped throughout with
an automatic sprinkler system, the hose connections are allowed to be
supplied from the automatic sprinkler system and shall have a flow rate of
not less than that required by NFPA 14 for Class III standpipes.*



2006 EDITION

*905.3.4 Exception:  Where the building or area is equipped throughout with
an automatic sprinkler system, a 1½ -inch (38mm) connection shall be
installed in accordance with **NFPA 13 or NFPA 14 for Class II or III
standpipes.*



Mark

Sprinkler Technology Design



On 2/21/07, Joe Burtell <[EMAIL PROTECTED]> wrote:

It is a stage per the building code 2003 IBC by definition. No platforms
here.

Joe Burtell, SET, CFPS
Burtell Fire Protection, Inc.
[EMAIL PROTECTED]
www.burtellfire.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Wednesday, February 21, 2007 11:23 AM
To: [email protected]
Subject: RE: Stage Standpipe System


Joe,
is it a stage or a platform in the auditorium? Will there be any scenery
used for the performances?
Sima


This e-mail and any attachments are confidential. If you receive this

message in error or are not the intended recipient, you should not retain,

distribute, disclose or use any of this information and you should destroy

the e-mail and any attachments or copies.











            "Joe Burtell"
            <[EMAIL PROTECTED]
            .com>                                                      To
            Sent by:                  <[email protected]>
            sprinklerforum-bo                                          cc
            [EMAIL PROTECTED]
            er.org                                                Subject
                                      RE: Stage Standpipe System

            02/21/2007 09:55
            AM


            Please respond to
            [EMAIL PROTECTED]
             resprinkler.org






Steve, I am talking with the AHJ today and I can show him the path I took
through the codes to get to the class I but do you have anything more in
NFPA 14? If it is just a class I does that also mean all of the rules for
a
class I apply like the cabinets are no longer needed ( when it was a class
III)?

Joe Burtell, SET, CFPS
Burtell Fire Protection, Inc.
[EMAIL PROTECTED]
www.burtellfire.com

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Steve
Leyton
Sent: Tuesday, February 20, 2007 6:22 PM
To: [email protected]
Subject: RE: Stage Standpipe System

I would say that you can put two manual Class I connections in place of
the
Class III by taking the sprinklered building exception.  If it was my
building or I was the AHJ, I wouldn't want the hoses in place.   But if
you
go that route, you would have to separate the sprinkler and standpipe
components under separate shut-off valves.

Steve L.

Just my opinion, not an interp, no cash value.


-----Original Message-----
From:        Joe Burtell [mailto:[EMAIL PROTECTED]
Sent:        Tue 2/20/2007 1:45 PM
To:          [email protected]
Cc:
Subject:           Stage Standpipe System

I have a stage that is over the 1,000 s.f. limit, the proscenium opening
is
less than 50', and it is a fully sprinklered building. Ok, here goes, 2003
IBC requires a class 3 standpipe system on each side of the stage. 2003
NFPA
14 says class 2 & 3 shall be automatic or semiautomatic wet 5.4.3. Section
7.3.4 says if the building is fully sprinklered I can do away with the
class
2 if ok by the AHJ. Now do I still have a class 3 or is it now just a
class
1 for the basis of whether I need an automatic supply?

Joe Burtell, SET, CFPS
Burtell Fire Protection, Inc.
[EMAIL PROTECTED]
www.burtellfire.com




_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum




_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to