Spot-on with the wax, Todd.  Back in the day, at the first contracting firm I 
worked for we dipped our own.  Used to buy paraffin in 5 lb. blocks from a 
candle and craft supply.   There are coatings that will adequately protect pipe 
and fittings; some would say that well-applied layers of primer and paint will 
protect as well as hot-dip if the latter isn't installed with care.  But it's a 
time-consuming exercise to paint all the exposed pipe ...

Steve Leyton
Protection Design & Consulting
Sunny, Salty, San Diego CA 

-----Original Message-----
From: Todd Williams - work [mailto:[EMAIL PROTECTED]
Sent: Wednesday, February 28, 2007 1:14 AM
To: [email protected]
Subject: Re: Seaside corrosion effect


Dan, the only thing I have seen (or used) that seems to work reliably 
is galvanized pipe and fittings and wax coated sprinklers

At 02:10 AM 2/28/2007, you wrote:
>I would appreciate the members' opinion regarding the type of coating that
>would provide the best corrosion protection for near seaside installation.
>
>Dan
>
>Dan Arbel Risk Eng
>T:  +972 (04) 8243337
>F:  +972 (04) 8243278
>M: +972 (052) 2810593
>
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to