See the appendix Figure A.5.19.3.4(2) in NFPA 20 2007 edition for the method
I used. I need 43 psi at required pump discharge.

The pump is rated @ 185 psi @ 750 gpm. At 150% flow we will have approx. 120
psi at pump discharge. 

Am I looking at this wrong or does this mean that we basically need 163 psi
at pump discharge in order to get the 150% flow?

So if we have 43 psi flowing 1125 gpm at pump suction, we got it. If not, we
don't?

I can not think clearly anymore so let me know where I am wrong if I am
wrong.
Thanks,

Greg

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Tom Duross
Sent: Friday, March 02, 2007 3:22 PM
To: [email protected]
Subject: RE: fire pump test header size

What did you calculate for an outlet?  Just the manifold (5-10'), tee
(5-15'), nipple(?) and valve (5-25')?
At what flow per 2.5" outlet?  250 per?  What happens when you put
50-75-100' of hose, playpipe, monster or meter on it?
I'm sure the upsize rule is to minimize friction loss.  If it's in the
standard, it must be done.

Interesting thing I just noticed this afternoon.  I just got home from an
acceptance test just now.
I used 4 digital flowmeters on a derby cap for a 1500 GPM diesel.  They have
pressure gauges on them for FDV testing.
We had a gauge on the 8" to the derby with (6) 2.5" angle valves just inside
the wall at the butterfly header valve.
At 2250, we had a 16 PSI drop from the gauge on the 8" to the gauges on the
meters.  I thought that was substantial.
We pretty much balanced the flow between the four meters but a drop that
great was surprising to me.
3' of 8" to a derby (this is like a bullhead tee hydraulically I would
imagine) and a 2.5x5 nipple and angle valve.
16 PSI at roughly 550 GPM.  I thought this to be substantial and they all
read the same and are almost new.

Tom Duross


Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852
This is from the 2007 edition of NFPA #20.

5.19.3.4 Pipe Size. The pipe size shall be in accordance with one of the
following two methods:

(1)      Where the pipe between the hose valve header and connection to the
pump discharge pipe is over 15 ft (4.5 m) in length, the next larger pipe
size than required by 5.19.3.1.3 shall be used.

(2)*      This pipe is permitted to be sized by hydraulic calculations based
on a total flow of 150 percent of rated pump capacity, including the
following:

(a)      This calculation shall include friction loss for the total length
of pipe plus equivalent lengths of fittings, control valve, and hose valves,
plus elevation loss, from the pump discharge flange to the hose valve
outlets.

(b)      The installation shall be proven by a test flowing the maximum
water available.


I just calculated a test header located approx. 65' from a 750 gpm pump and
it seems to work easily with 6" pipe flowing 1,125 gpm in lieu of increasing
the pipe to 8". Has anyone got experience using this method?

Space is the issue and 6" works much better then 8" in this situation.


Thanks,
Greg McGahan


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to