Thank you Thom, that is an excellent proposal. 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom McMahon
Sent: Monday, March 05, 2007 9:33 AM
To: [email protected]
Subject: Re: Reduced Calc Areas

I think that this is a unique situation which I would discuss with the AHJ. 
In the past with a similar small lobby and open hall, we have calculated the
heads in the lobby and up to 7 heads in the hall. NFPA 13 2002 11.2.3.3.8

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message -----
From: "Kathryn Tyler" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Monday, March 05, 2007 8:06 AM
Subject: RE: Reduced Calc Areas


>I do realize that, but what if the areas in the remote areas contain heads
> in the corridor which is open at one point to the waiting room which has a
> ceiling exceeding 20' ion height?  Would I then calc the existing areas
> utilizing the % reduction and then calc the high ceiling and surrounding
> areas at 1500 sq ft?  Even when there are only 2 heads covering the area
> with the high ceiling?
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Scott
> Mitchell
> Sent: Friday, March 02, 2007 5:29 PM
> To: [email protected]
> Subject: RE: Reduced Calc Areas
>
> Chris: No - but it would be the AHJ's prerogative to require a separate
> hydraulic calculation for the mechanical room.
>
>  Kathryn: Your hydraulic calculation using a QR design area reduction is
> only valid for those portions of the building with ceiling heights used to
> set the % reduction. If an area's ceiling height exceeds that, you have to
> do a separate calculation for that area.
>
>  Regards,
>  Scott Mitchell
>
> Chris Brown <[EMAIL PROTECTED]> wrote:
>  Would you space all the sprinklers 130 sq. ft. throughout because of a
> mechanical room with the building.
>
>
> Thank you,
>
> Chris Brown
> Fire Protection Designer, Poole Fire Protection
> Office: 913.829.8650 Direct: 913.747.2056 Cell: 913.208.3600 Fax:
> 913.829.8690
>
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Kathy Tyler
> Sent: Friday, March 02, 2007 9:31 AM
> To: [email protected]
> Subject: Reduced Calc Areas
>
> Our firm has a job where two of the designers (co-working on the
> project) in my office made a decision to not reduce the hydraulic calc 
> area
> per using Quick Response heads because of a small waiting area that is 
> open
> to both floors, (this building has only 2 stories) which would make the
> ceiling height exceed 20' as allowed. However I am reviewing the design
> prior to going out and I am questioning their decision and would 
> appreciate
> the Forums feedback.
> There is an area at the entry of the bldg and it is 162 sq. ft. and is not
> included in any of the two remote areas on the 2nd floor being calculated.
> However the remote areas do include heads in the corridor which is open to
> the waiting area which has the high ceiling.
> Do you feel that because of this high area that all calculations should 
> not
> be allowed to be reduced or should be?
> Thank you in advance,
> Kathryn
>
> Kathryn A. Tyler NICET IV, ASCET Member
> fire protection designer
> Kelly-Wright & Associates PC
> Hvac, Plumbing & Fire Protection
> (520) 887-1919 ext. 302
> fax: (520) 696-0280
> [EMAIL PROTECTED]
> www.kwmech.com
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>
>
> ---------------------------------
> Bored stiff? Loosen up...
> Download and play hundreds of games for free on Yahoo! Games.
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> 


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to