In order to omit from the calculations such small rooms (with light fuel loads as already discussed but poorly defined), you must have a remote area with a minimum size from Figure 11.2.3.1.1 (ie 1500 sf for LH & OH) plus any increases. IT identifies 30% for dry pipe but ceiling slope would also apply as would the EC specific minimum number. The reduction for QR can NOT be applied. I submited a proposal on this an the TC explicitly addressed this aspect (ROP 633).

The area for the small room is included in sizing the remote area.

There are no defined requirements for the wall construction. This equates to it NOT being required to be fire rated construction (or it would explicitly state that). I would take the guidance on walls from the criteria on adjacent occupancies which requires the walls to simply be capable of stopping heat. This is obviously considered to be standard construction and not paper partitions.

Roland

On Mar 8, 2007, at 8:23 AM, Kathy Tyler wrote:

Good Morning Forum,  I am currently reviewing a project which is
utilizing the Tyco EC-11 extended coverage pendent heads. I have rarely
used them and could use your great input.
My question is:
The calculation area is a kitchen and in the center of the kitchen are
three rooms, toilet,offices (which have 5.6 heads in them) the
calculation area for the ext. cov. pendents includes these rooms, put
are being omitted per 14.4.4.4.2.  Can or should the calculation area
include these rooms as square footage or should you exclude them and
pick up square footage from the areas which have ext. cov. hds?
Thank you in advance for all help,
Kathryn

Kathryn A. Tyler NICET IV, ASCET Member
fire protection designer
Kelly-Wright & Associates PC
Hvac, Plumbing & Fire Protection
(520) 887-1919 ext. 302
fax: (520) 696-0280
[EMAIL PROTECTED] <blocked::mailto:[EMAIL PROTECTED]>
www.kwmech.com <blocked::http://www.kwmech.com/>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to