In order to omit from the calculations such small rooms (with
light fuel loads as already discussed but poorly defined), you must
have a remote area with a minimum size from Figure 11.2.3.1.1 (ie
1500 sf for LH & OH) plus any increases. IT identifies 30% for dry
pipe but ceiling slope would also apply as would the EC specific
minimum number. The reduction for QR can NOT be applied. I submited
a proposal on this an the TC explicitly addressed this aspect (ROP 633).
The area for the small room is included in sizing the remote area.
There are no defined requirements for the wall construction. This
equates to it NOT being required to be fire rated construction (or it
would explicitly state that). I would take the guidance on walls
from the criteria on adjacent occupancies which requires the walls to
simply be capable of stopping heat. This is obviously considered to
be standard construction and not paper partitions.
Roland
On Mar 8, 2007, at 8:23 AM, Kathy Tyler wrote:
Good Morning Forum, I am currently reviewing a project which is
utilizing the Tyco EC-11 extended coverage pendent heads. I have
rarely
used them and could use your great input.
My question is:
The calculation area is a kitchen and in the center of the kitchen are
three rooms, toilet,offices (which have 5.6 heads in them) the
calculation area for the ext. cov. pendents includes these rooms, put
are being omitted per 14.4.4.4.2. Can or should the calculation area
include these rooms as square footage or should you exclude them and
pick up square footage from the areas which have ext. cov. hds?
Thank you in advance for all help,
Kathryn
Kathryn A. Tyler NICET IV, ASCET Member
fire protection designer
Kelly-Wright & Associates PC
Hvac, Plumbing & Fire Protection
(520) 887-1919 ext. 302
fax: (520) 696-0280
[EMAIL PROTECTED] <blocked::mailto:[EMAIL PROTECTED]>
www.kwmech.com <blocked::http://www.kwmech.com/>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum