7+2 not 7 total. (9 Total)
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message -----
From: "Reed Roisum" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Thursday, March 08, 2007 10:47 AM
Subject: Calculating Attic Heads
I am reviewing a dry system attic layout using Tyco's Single Directional
(SD) and Back to Back (BB) attic heads. The attic narrows at the remote
area so that the peak goes from an attic peak (12/4 slope)with roof on
each side, to a roof only on one side of the peak. (sorry for the poor
description, it would make sense if you could look at the plan).
What is important to my question is that the 3 most remote heads are SD
heads and then it continues with BB's along the peak. The cut sheets on
these specific application sprinklers say when you have BB's and SD's to
calculate the 7 most demanding BB sprinklers plus up to 2 SD sprinklers.
But, the example figure shows a little different scenario than what I
have.
The technician who laid this out calc'd the 7 most remote sprinklers (3
SD's and 4 BB's). I'm thinkin' that is not right. It looks to me as
though the 7 most remote BB's and the adjacent 2 SD's should be calc'd.
Maybe we are both wrong??
Any guidance will be appreciated.
Reed A. Roisum
Fire Protection Technician
Ulteig Engineers, Inc.
3350 38th Avenue South
Fargo, ND 58104-7079
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum