Hi Greg, I know in our town we enforce installation of a full fire alarm, (horns, strobes etc...)based on the fact that we have adopted the Illinois Accessibility code.NFPA 72 just tells you how it shall be installed. I would check with your state ADA requirements. I hope this helps.
-----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Tim Frankenberg Sent: Wednesday, March 07, 2007 5:50 PM To: [email protected] Subject: Re: audible alarms Greg, Based on the IFC that we have, a fire alarm system is required only if the occupant load on the second floor exceeds 100. Since automatic sprinklers are present, the need for a manual fire alarm system is exempted. The only required audible alarm is a water flow signal located on the outside of the building. If the owner opted to install a non-required fire alarm system (manual pull stations, smoke detectors, duct detectors, etc), then the story changes a bit. Then an audible signal must be heard in all parts of the building and that dumps you over to NFPA 72 and the fire alarm code. The minimum is a communicator to send a signal of waterflow (alarm), a trouble (power or phone line failure) or a supervisory condition (valve tamper, low temperature, etc.). A smoke detector is required above the panel and a single pull station to satisfy the requirements of NFPA 72. The installation of those two initiating devices does infer that a complete system is installed. The recent NFPA 72 was changed because of the very issue of a the pull and smoke leading AHJ's to force a complete alarm system when it was not really required. Hope that helps. Tim Tim Frankenberg, CFPS Fire/Security Product Manager Potter Electric Signal Company www.pottersignal.com 800-325-3936 >>> [EMAIL PROTECTED] 3/7/2007 5:16 pm >>> We do not install alarms and have very little knowledge in this area. Can someone tell me if an audible alarm is required to be provided throughout an occupied building equipped with a sprinkler system? The building in question was a shell building, 2 story, retail below (after buildouts) and offices above. We are providing sectional control valves for convenience in each tenant space. There is a flow switch on the main riser for the entire building and an existing audible alarm installed when the shell building was installed. Now there is an alarm contractor claiming that each space is required to have a flow switch and that no horns/ strobes are required in the spaces? The entire building is approximately 30,000 sq ft (15 per floor). Thanks for the help, Greg Living Water Fire Protection, LLC 1160 McKenzie Road Cantonment, FL 32533 850-937-1850 Fax: 850-937-1852 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum