Hi Greg,
I know in our town we enforce installation of a full fire alarm, (horns,
strobes etc...)based on the fact that we have adopted the Illinois
Accessibility code.NFPA 72 just tells you how it shall be installed. I
would check with your state ADA requirements. I hope this helps.


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Tim
Frankenberg
Sent: Wednesday, March 07, 2007 5:50 PM
To: [email protected]
Subject: Re: audible alarms

Greg,

Based on the IFC that we have, a fire alarm system is required only if
the occupant load on the second floor exceeds 100. Since automatic
sprinklers are present, the need for a manual fire alarm system is
exempted. 

The only required audible alarm is a water flow signal located on the
outside of the building. If the owner opted to install a non-required
fire alarm system (manual pull stations, smoke detectors, duct
detectors, etc), then the story changes a bit. Then an audible signal
must be heard in all parts of the building and that dumps you over to
NFPA 72 and the fire alarm code. 

The minimum is a communicator to send a signal of waterflow (alarm), a
trouble (power or phone line failure) or a supervisory condition (valve
tamper, low temperature, etc.). A smoke detector is required above the
panel and a single pull station to satisfy the requirements of NFPA 72.
The installation of those two initiating devices does infer that a
complete system is installed.

The recent NFPA 72 was changed because of the very issue of a the pull
and smoke leading AHJ's to force a complete alarm system when it was not
really required. 

Hope that helps.

Tim

Tim Frankenberg, CFPS
Fire/Security Product Manager
Potter Electric Signal Company
www.pottersignal.com
800-325-3936

>>> [EMAIL PROTECTED] 3/7/2007 5:16 pm >>>
We do not install alarms and have very little knowledge in this area.
Can
someone tell me if an audible alarm is required to be provided
throughout an
occupied building equipped with a sprinkler system?

The building in question was a shell building, 2 story, retail below
(after
buildouts) and offices above.

We are providing sectional control valves for convenience in each tenant
space. There is a flow switch on the main riser for the entire building
and
an existing audible alarm installed when the shell building was
installed.
Now there is an alarm contractor claiming that each space is required to
have a flow switch and that no horns/ strobes are required in the
spaces?

The entire building is approximately 30,000 sq ft (15 per floor).

Thanks for the help,
Greg

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852



_______________________________________________
Sprinklerforum mailing list
[email protected] 
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to