> -----Original Message-----
> From: [EMAIL PROTECTED] [mailto:sprinklerforum-
> [EMAIL PROTECTED] On Behalf Of Garth W. Warren
> Sent: Friday, March 09, 2007 4:12 PM
> To: [email protected]
> Subject: Re: Pandora's Box
> 
> Does anyone know how much pressure would it take to push 35 gpm through a
> 3/4" meter?
> 
> Thanks -
> Garth
> ----- Original Message -----
> From: "PCE" <[EMAIL PROTECTED]>
> To: <[email protected]>
> Sent: Friday, March 09, 2007 2:01 PM
> Subject: Re: Pandora's Box
> 
> 
> Chris,
> 
> Badger makes a meter, model M40, which is 3/4 x 3/4, and their chart
> shows that it can accept flows of up to 35 gpm.  And, at that flow, it
> has a pressure loss of around 6.5 to 7.0 psi.  I would think that would
> certainly be sufficient to not impact the design of a residential system
> at the same level as the chart losses shown in NFPA-13D.
> 
> Out here, the AHJ's are starting to require the designers [sue me if you
> don't like that word] to submit the data on the meter along with the
> calculations and plans.
> 
> Just one more item to check prior to submittal.
> 
> PARSLEY CONSULTING
> Ken Wagoner, SET
> 760.745.6181 voice
> 760.745.0537 fax
> [EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail
> www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website
> 
> 
> 
> 
> Chris Brown wrote:
> > Thank you for the information and now we have another manufacturer a
> > meter of with the same results as described in my last email, a 5/8 inch
> > or 3/4 inch will not meet the flow requirements of a lot of the NFPA 13D
> > and NFPA 13R systems. IF as the AHJ, designer or installer of such
> > systems you should be thinking pretty hard right now.
> >
> >
> > Thank you,
> >
> > Chris Brown
> > Fire Protection Designer, Poole Fire Protection
> > Office: 913.829.8650   Direct: 913.747.2056   Cell: 913.208.3600   Fax:
> > 913.829.8690
> >
> >
> > -----Original Message-----
> > From: [EMAIL PROTECTED]
> > [mailto:[EMAIL PROTECTED] On Behalf Of Kathryn
> > Tyler
> > Sent: Friday, March 09, 2007 11:40 AM
> > To: [email protected]
> > Subject: RE: Pandora's Box
> >
> > This is the water meter we use here a lot.
> > http://www.badgermeter.com/pdf/recdisk/tech/rd-t-34.pdf
> >
> > http://www.vikinggroupinc.com/databook/sprinklers/residential/103105.pdf
> > is an example of a concealed head that could work with up to 16x16
> > spacing (flat ceilings only though - if on sloped clgs, the press.
> > requirement goes way up) There are others that will work, but this is an
> > example. Generally, it is tough to go more than 16x16 spacing with a
> > 3/4" meter, unless the run of copper between the tap and meter is very
> > short, the water pressure is very high. (Don't forget the loss through
> > the pipe between the tap and meter must be included in the calcs) Many
> > have requested for only 1" meters to be installed now, which is a lot
> > more expensive.
> > Kathryn
> >
> >
> > -----Original Message-----
> > From: [EMAIL PROTECTED]
> > [mailto:[EMAIL PROTECTED] On Behalf Of PCE
> > Sent: Friday, March 09, 2007 8:48 AM
> > To: [email protected]
> > Subject: Re: Pandora's Box
> >
> > Chris,
> >
> > They would have the same effect that any valve or fitting would have on
> > the ability of a sprinkler system to function properly.  The loss in
> > pressure due to friction at various flows through the meters is required
> > to be accounted for in the hydraulic calculations.  Interestingly
> > enough, NFPA-13D tells us that the actual chart loss from the meter
> > manufacturer should be reviewed during the calculation process.  If the
> > chart loss is lower than those figures in the table in 13D it may be
> > used, however the standard also says that if the chart loss from the
> > manufacturer is greater than those shown in the table that the higher
> > value MUST be used.
> >
> > Out here we see hundreds of residential sprinklers systems every month,
> > and for the most part they utilize 1" meters.  With a 13 gpm demand per
> > sprinkler, and a 5 gpm allowance for domestic use, the system flow of 31
> > gpm exceeds the values shown in 13D as acceptable for a 5/8", and is
> > right on the line at the maximum allowed for a 3/4".
> >
> > There has been much shouting regarding the issue of meter size out here,
> > and most of it accompanied by vague suggestions of dire consequences and
> > thousands of dollars needlessly wasted if one position or another isn't
> > followed.
> >
> > What is your take on the issues involved?
> >
> > PARSLEY CONSULTING
> >
> > Ken Wagoner, SET
> >
> > 760.745.6181 voice
> >
> > 760.745.0537 fax
> >
> > [EMAIL PROTECTED] <mailto:[EMAIL PROTECTED]> e-mail
> >
> > www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website
> >
> >
> >
> >
> > Chris Brown wrote:
> >
> >> Question to the forum:
> >> What effect does a 5/8 inch or 3/4 inch water meter have on fire
> >> sprinkler
> >>
> > system installed in an NFPA 13D or NFPA 13R system. The issue is one of
> > the maximum continuous flow thru the meter and its effect on the ability
> > of the fire sprinkler system to operate as intended. I respectfully
> > request, Please research and answer after you have visited with the
> > water meter manufacturer's and or water departments as I have already
> > done. Keep in mind that a single residential sprinkler has a minimum of
> > some where between 19 and 25 gpm requirements and that most dwellings
> > have two sprinklers flowing in the hydraulically remote area.
> >
> >>
> >> This will be fun for a Friday:)
> >>
> >> Thank you,
> >>
> >> Chris Brown
> >> Fire Protection Designer
> >> Please note our new company name, e-mail address and web site.
> >>
> >>
> >>
> >> innovative leader    $B"%(J     trusted partner
> >>
> >> 19910 West 161st Street
> >> Olathe, KS  66062
> >> Office:  913.829.8650
> >>
> >> Direct:
> >> Cell:
> >> Fax:
> >>
> >> 913.747.2056
> >> 913.208.3600
> >> 913.829.8690
> >>
> >> www.poolefire.com <http://www.poolefire.com/> Office Map
> >>
> <http://www.mapquest.com/maps/map.adp?address=19910%20W%20161st%20St
> &c
> >> ity=Olathe&state=KS&zipcode=66062-
> 2700&country=US&title=%3cb%3e19910%2
> >> 0W%20161st%20St%3c/b%3e%3cbr%20/%3e%20Olathe,%20KS%2066062-
> 2700,%20%20
> >> US&cid=lfmaplink2&name=>
> >>
> >> This e-mail, and any files transmitted with it, are confidential and
> >>
> > intended solely for the use of the individual or entity to which they
> > are addressed.  If you have received this e-mail in error, please notify
> > [EMAIL PROTECTED]
> >
> >>
> >>
> >>
> >> ----------------------------------------------------------------------
> >> --
> >>
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>
> >> ----------------------------------------------------------------------
> >> --
> >>
> >> No virus found in this incoming message.
> >> Checked by AVG Free Edition.
> >> Version: 7.5.446 / Virus Database: 268.18.8/714 - Release Date:
> >> 3/8/2007 10:58 AM
> >>
> >>
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >
> >
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> --
> No virus found in this incoming message.
> Checked by AVG Free Edition.
> Version: 7.5.446 / Virus Database: 268.18.8/714 - Release Date: 3/8/2007 10:58
> AM
> 

-- 
No virus found in this outgoing message.
Checked by AVG Free Edition.
Version: 7.5.446 / Virus Database: 268.18.8/714 - Release Date: 3/8/2007 10:58 
AM
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to