Although, speaking of the spacing within a small room... This has been as
issue of debate between 'designers' or layout fire protection people for
quite some time. 
To play the devil's advocate here; if you are allowed to move one head 1-1/2
ft to making it 9 foot off the wall and you are allowed to go 15 foot to the
next head and that head is allowed to be a max. of 6 foot off the wall
(because 15' - 9' = 6'), isn't the head that is 6' off the wall still
covering 7'-6" in the opposite direction.  225 sq. ft. divided by 18' =
12'-6" not 12'-0", so why the 6'-0" ruling? 