Guys, there is (categorically) NO SUCH THING as a Cla-Valve.  That is the name 
of a manufacturer.   We don't call sprinklers a Tyco or a Viking, do we?  What 
KIND of Cla-Valve?  They make every type of hydraulic control valve imaginable 
...  Sorry to be so anal-retentive, but terminology is everything on this 
subject. 

SL

-----Original Message-----
From: Ed Kramer [mailto:[EMAIL PROTECTED]
Sent: Wednesday, March 14, 2007 12:00 PM
To: [email protected]
Subject: RE: pump tricks


Todd, the Cla Valve may be fully open (or close to it) all the time.
Combine the flow test at nowhere close to what you should be seeing, with
steam coming from the diesel, makes me think you've got a whole lot of
water being pumped in a circle and overheating.  The cooling water for the
diesel engine likely comes from the suction side of the pump and is pulling
in that overheated water. 

Ed Kramer
Littleton, CO

>
>The situation I have is that the main relief valve was replaced with
>a Cla Valve (called the contractor to confirm) which discharges back
>into the suction line. We can't be sure if this is operating properly
>or is even set right.This entire pump arrangement is going to be
>reviewed, repaired and re-designed. The valve is actually (I think) a
>minor part of the problem. The initial hydrant test on the yard loop
>yielded 630 gpm at 30 psi from a 1500 at 125 pump and steam was
>shooting out of the engine.



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to