'Let's Get Ready To Rumble'...

Happy St. Patrick's Day!!! Just don't get pinched on a designing a system
without a good enough safety margin!

Kathryn

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron
Sent: Friday, March 16, 2007 8:19 AM
To: [email protected]
Subject: RE: Re[2]: Mininum Supply Pressure

Yeah, now we're getting to the good stuff. Ideally a safety margin is a good
thing. Asking an owner to spend $50k to add a pump IMHO shows a real lack of
imagination. If it complies with code who are we to say "I know better"? It
takes a PE to know that NFPA, IBC, IFC and the local AHJ are all wrong.
Surely no layout technician would say they know better than the codes.

In honor of St. Patrick's I though I would try to start a fight. 

Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Brian Harris
Sent: Friday, March 16, 2007 8:00 AM
To: [email protected]
Subject: RE: Re[2]: Mininum Supply Pressure

That may be a blessing in disguise, let them put their neck on the line.
If I ain't got 10% it ain't going in, period.

           Regards,
              Brian Harris
First Defense Fire Protection
        Design Engineer
   [EMAIL PROTECTED]
           704.948.3506 phone
           704.948.3507 fax

 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Charles
Thurston
Sent: Friday, March 16, 2007 11:49 AM
To: [email protected]
Subject: Re[2]: Mininum Supply Pressure

Hello All,

Well this all started when I did not have any excess pressure for a safety
margin and informed the General Contractor a small fire pump would be
required. He decided to take the drawings to another sprinkler contractor
for a second opinion, This other sprinkler contractor stated it could be
done without a pump. At this time the owner of the company I work for and
the general contractor decided to sub out a "redesign" of the system to this
other sprinkler contractor (we still get to do the install). This other
sprinkler company supplied the drawings, calcs, COC, and Spec sheets.

Friday, March 16, 2007, 9:40:29 AM, you wrote:

> Yet another case of calculate with a computer, measure with a 
> micrometer, mark with a piece of chalk and chop off with an axe.

> Ron Fletcher
> Aero Automatic
> Phoenix, AZ

> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Charles

> Thurston
> Sent: Friday, March 16, 2007 7:19 AM
> To: [email protected]
> Subject: Mininum Supply Pressure

> Hello All,

> Let me be the one to start things today.

> What is the minimum safety pressure allowed ? I have looked in 13 and 
> did not find it....  I have a situation where the safety pressure is
> 0.913 psi.

> Basis is:
>  Hose 250
>  Static 67.00
>  Residual 38.00 @ 920.00
>  Available 40.128 @ demand of 882.87
>  Requires 39.215 psi
>  Leaving a safety of 0.913 psi
>  

> --
> Best regards,
>  Charles                          mailto:[EMAIL PROTECTED]
> Coastal Fire Protection

> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum



--
Best regards,
 Charles                            mailto:[EMAIL PROTECTED]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to