Keep in mind that 13 has relaxed its position on bushings in branch
lines to accommodate future modifications - see 8.15.19.2. This is
not limited to installing uprights while we wait for the drop ceiling
to be installed.
Roland
On Mar 12, 2007, at 11:34 AM, Paul Pinigis wrote:
Nope. These are not bushings for sprinklers connected directly to
branch lines for future accommodation of a suspended ceiling, and
standard fittings of the required size were available, so neither
of the
exceptions applies.
These are bushings that were installed by the contractor for
simplicity
in construction, not because they met any of the design criteria.
Paul J. Pinigis, P.E.
Chief Life Safety Engineer
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Posey,
Mike
Sent: Monday, March 12, 2007 2:24 PM
To: [email protected]
Subject: RE: Equivalent length of bushings
NFPA 13, 2002 edition......
6.4.6.2 Hexagonal or face bushings shall be permitted....
6.4.6.3. Hexagonal bushings as permitted.......
USE OF BUSHINGS IS ALLOWED
Mike Posey
Direct: 972-587-5232
[EMAIL PROTECTED]
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Paul
Pinigis
Sent: Monday, March 12, 2007 1:03 PM
To: [email protected]
Subject: Equivalent length of bushings
Does anyone out there know where I can find the equivalent length of
various bushings that were installed in a system. I know that NFPA 13
does not permit the use of bushings, and that they do not require
additional equivalent length to be added to the calculations for the
bushings, but I would like to include them in our calculation for
peace-of-mind.
Paul Pinigis
Hankins and Anderson
Consulting Engineers
4880 Sadler Road Suite 300
Glen Allen, VA 23060
v: (804) 285.4171 f: (804) 217.8520
http://www.haengineers.com
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum