Bill,

The number of rings that operates is a function of the occupancy. In a light hazard occupancy, a fire will not operate sprinklers byond the second ring unless something goes wrong. In more challenging occcupancies, you get into the third, or even fourth wring, even if nothing goes wrong.

The curves for claa I-IV are a very special case. They were developed from testing in the late 60's and early 70's, when most existing sprinkler system were simple pipe schedule designs. It was deemed necessary to provide curves to allow as many existing systems to be evaluated as possible. A curve was developed from testing of class II commodity at a variety of densities. As would be expected, the number of sprinklers that operated went down as the density went up. No safety factor was applied to the curve. Each test was plotted as an unadjusted point. Two tests of class III commodities were performed, and a curve parallel to the class II curve was plotted through those two points. Two test were performed on a class IV commodity, and the curve was plotted the same way. The class I curve was drawn without any tests. It's not pretty, but there you have it!

You will note that no protection requirements based on actual testing subsequent to the class I-V tests have involved curves.

The reason that designs based on the curves have worked so well is that they were based on tests using K5.6 sprinklers and the design requirements were specified as densities and areas. As we have subsequently learned, discharge density is not a fundamentel measure of sprinkler performance. A 0.30 density is significantly more effective from a K8.0 sprinkler than from a K5.6, and far more effective from a K11.2 sprinkler. Economics have made the larger K-factors the normal choice. That's the safety factor we have now.

Joe



Brooks, Bill wrote:

I laid out a 11.4 x 11.4 pattern (130 sq ft) and drew three rings.  1st ring
included 4 sprinklers (520 sq ft).  2nd ring included 12 sprinklers (1520 sq
ft).  3rd ring included 24 sprinklers (3120 sq ft).  The numbers are
comparable to NFPA ~1500 sq ft and the DoD ~ 3000 sq ft.

The ring theory makes sense in this context.  NFPA is looking for a two ring
design and DoD is looking for a three ring design?  Was this purposeful?  If
so it provides the basis for the 1500 sq ft minimum design area.

Using this approach, the 900 sq ft design looks like it has a very small
margin of error.

If we have this two ring NFPA design, what led to the development of the
area/density curves where density is decreased as design area is increased?

Bill Brooks
Pittsburgh, PA

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] Behalf Of Joe
Hankins
Sent: Friday, March 16, 2007 2:49 PM
To: [email protected]
Subject: Re: Burning Ring of Fire (and the Flames Shot Higher)


Bill,

You are correct. Sometimes politics prevails.

Joe

Brooks, Bill wrote:

Joe,

I thought I understood your train of thought until I started considering
the
area reduction for quick response sprinklers.  How many rings are there
with
a 10 ft ceiling height QR design?  900 sq ft or 5 heads.

Can I conclude the ring theory falls apart when this design approach is
used?  It looks like you don't have your 1 ring cushion in this case.

Bill Brooks
Pittsburgh, PA

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] Behalf Of Joe
Hankins
Sent: Friday, March 16, 2007 11:56 AM
To: [email protected]
Subject: Re: Minimum Supply Pressure

The idea that there is a huge difference between a 5-sprinkler fire and a 15- or 30-sprinkler fire seems logical on the surface, but if you know how sprinklers operate, you know they operate in rings. The heat that operates sprinklers spreads in a circle from the fire origin. For symetrically-spaced sprinkler system where the fire starts centered among 4 sprinklers, there are 4 sprinklers in the first ring around ignition, so there is virtually no difference between a 1-sprinkler fire and a 4-sprinkler fire. If those sprinklers don't control the fire, then any (and all) of the 12 sprinklers in the next ring can operate, meaning that there is very little difference betwen a 5-sprinkler fire and a 16 sprinkler fire. If you get into the next ring, then the number is 36 sprinklers. So, the 1-ring "safety factor" between 4 and 16 sprinklers is the same as the 1-ring safety factor between 16 and 36 sprinklers. A 1-ring "safety factor" is not overkill in my book!
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum




_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to