Let me explain this project a little more, because I think I'm being
misunderstood.  We are sprinklering a new addition of a sawmill production
floor.  There is a lower floor and a main floor in the new addition.  On the
main floor of the addition there is a mezzanine.  The mezzanine has a solid
floor, and is completely open to the surrounding area (above and below).  So
essentially, in one room, over one floor area, we have two areas being
sprinklered.  The first is below the mezzanine.  The second is at the roof
deck.  The area of the roof deck will not meet the square footage
requirements of my extra hazard occupancy (3250 sqft. with dry penalty).  So
my question is, do I need to calculate heads under the mezzanine to meet my
square footage requirements, or will a calc of the heads at the roof deck be
sufficient.   


Jimmy Waite
Burtell Fire Protection, Inc.
[EMAIL PROTECTED]
406-652-7697



-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Jimmy Waite
Sent: Monday, March 26, 2007 1:54 PM
To: [email protected]
Subject: Mezzanine Calcs. 


Dear Forum, 

We are currently working on a project where we are tying onto a dry, gridded
sprinkler system, installed in 1985.  There are two existing dry systems and
they each cover an area of about 13,100 square feet.  The lower floor is a
tree system that was sized by "Table 3-7.1" of NFPA 13, 1984 Ed.  The main
floor is a grid that was designed at a .275/ 3000 square feet with 500 gpm
hose allowance.  The addition that we are sprinklering is only 2,000 square
feet.  On the main floor of the addition there is a mezzanine of about 1,000
square feet.  Is a calculation even needed for such a small addition, or can
we use the existing pipe sizing as our guide?  If a calculation is required,
would we calculate the sprinklers along the roof deck by themselves, or do
we need to include the sprinklers under that mezzanine in our calculations
as well.  

Thanks for the help

Jimmy Waite
Burtell Fire Protection, Inc.
[EMAIL PROTECTED]
406-652-7697




_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to