Every system we design (Layout) has excessive flow, all you have to do is a
supply calc to see it. Our state requires a 10% or 10 Psi "Safety Factor"
Cushion on all designs (Layouts) That's all the way down the curve. You do a
light hazard layout with a reduction for QR and the overflow in a supply
calc can more than double the actual flow.
Additionally there are fabrication trade-off's. If your company likes to fab
and install using welded outlets, you may carry the 11/4" branchline all the
way to the last head, accepting the additional friction loss close to the
main or cross main, and usually ending up with the end sprinkler not being
the HMD. This will be an overflow for the system, that's acceptable to the
layout tech. since his boss doesn't want to see a lot of screw pipe on his
projects, or he just bought the new "Whirly Bird" welder, and wants to see
payback ASAP. Or maybe he got a great deal on a truck load of 11/4" sch 10
pipe he needs to use up. Or maybe it was all fabricated for another job,
where they changed the use before it was installed, and it's "Free" pipe.
If you only do "Layout" you may not have to consider all of these
possibilities, but as a layout tech for a contractor this is every day
stuff.
As an Engineer wanting to learn about Fire Sprinklers, I welcome you.
I've seen calc's and drawings from an engineer (Nucular) for a Ice arena
that were hand calc'ed and a thing of beauty! He also had 30 years of
experience, but it was just so hard to find that 31/2" pipe, and the 41/2"
and 51/2" were just impossible. (True Story) I just wish the hand calc's
I've done could look as nice as his! but then again, mine are at least in
available pie (or is that pipe) sizes.
I did not intend to be condescending, Usually just short on time, and spend
my days amazed at what these forum member's know, and it's usually right off
the top of their heads, while I need to spend hour's reading to get to the
same point or conclusion.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message -----
From: <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Tuesday, March 27, 2007 9:18 AM
Subject: RE: Selecting Heads For a New System
The biggest problem contributing to excessive flows in quite a few cases
is the designers often don't go back and tweak their pipe sizes, they
just let the calcs come out with whatever will work and if there's a
cushion at the end, they're done. Sometimes, a lot of times, a few
tweaks here and there can bring that system closer in line to what it
should be without a lot of excess flow. Remember some discussions in
the last couple of weeks where sprinkler contractors had been sued due
to excessive water damage? When your flowing 50,60,70% more than the
design calls for there is probably some tweaking room. But someone has
to know how to do it and be willing to take the time to do it. Ah,
there's the rub!
Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC 29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams - work
Sent: Tuesday, March 27, 2007 11:10 AM
To: [email protected]
Subject: RE: Selecting Heads For a New System
Brian,
First off, welcome to the club.
Secondly, does this mercantile space have a drop ceiling? If so, that
may dictate your spacing somewhat, especially if they want center of
tile.
Overages can be tricky; it depends a lot on the building configuration,
location of rooms, etc. A set of plans came across my desk yesterday
with a 0.15/900 demand, which would equate to a base of 135 gpm. The
demand flow in the sprinkler system is 229 gpm, almost a 70% overage. It
was completely appropriate based on the configuration. If I need to
estimate the water demand, what I like to do is lay out the sprinklers
first, using the ceiling plan and the NFPA standards. From there I would
locate the remote area, count the number of sprinklers in that area and
multiply it by the minimum flow. I would assign the overage from that
figure; typically 10% for grids and 25% for trees. (In the example I
cited above, there were 12 sprinklers at a flow of 18 gpm per sprinkler,
or a total of 216 gpm.
Therefore the actual flow of 229 gpm was only a 6% overage. My estimate
would have been 216 x 1.25 = 270 gpm.)
It's not an exact science, so accept it as that. I hope this helps.
Todd
Let me start by saying I've only been in the sprinkler world for just
over a year so if any thing I ask is "rookie-ish" please keep that in
mind. I'm looking for ideas that some of you may use when starting a
new project when it comes to selecting what heads (head spacing) to
use. For example: I am starting a retail store (mercantile) that has a
Static of 47 psi Residual of
42 psi, & flow of 1090 gpm. What I do now to get me "in the ballpark"
is take the density x area of operation x 1.4 (for overage) + hose
allowance.
That gets me roughly the system gpm demand. So .20 x 1500 = 300 x 1.4
= 420
+ 250 (hose) = 670 gpm. I then plot that gpm on my water supply curve
(N1.85) to get the psi for that gpm; in this case that's around 45psi.
From
that psi I take out for the BFP, elevation, 40% (friction loss & etc)
and whatever is left I find a head with an end head pressure that's
slightly under that and away I go.... Any thoughts? Suggestions? Better
Ideas?
Regards,
Brian Harris
First Defense Fire Protection
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum