As preached by Joe for some time, in defining the commodity
classification the overall percentages (per definitions) are
important but not the only parameters of interest. WHERE the plastic
is located is a critical aspect. If you have a metal item surrounded
with an expanded group A plastic, the overall pallet load can be less
than 15% by weight or 25% by volume and by definition a Class IV, but
it will still burn just like a Group A plastic. Conversely, you can
have almost all plastic surrounded by a metal casing that is
considered a Class II. This is discussed in the Annex (A.5.6 and A.
5.6.1.1) and the Handbook.
Roland
On Mar 27, 2007, at 12:25 PM, David Autry wrote:
Seed corn stored in high-density polyethylene totes. The totes are
approximately 5'x5'x5', completely enclosed (with lid) and are
stacked 3
high (15 ft total height). My first thought is NFPA 13 (2002)
5.6.2.3 where
if reinforced high-density polyethylene pallets are used, move up 2
commodity classes. These totes have roughly 5 times as much plastic
than a
pallet, so I'm not sure moving up 2 classes would be adequate
protection.
Anyone out there seen any of these?
Any thoughts?
David Autry
Plans Examiner
Nebraska State Fire Marshal's Office
246 S. 14th Street
Lincoln, NE 68508
402-471-9659
402-471-3118 fax
www.sfm.ne.gov