I would not test per NFPA 72.  You must test and maintain per the 
manufacturer's catalog/data sheets as they are specific to the systems involve 
- specifically, you  are looking for "Automatic" Sprinkler Corp of America 
Suprotex System (Deluge Sprinkler System) Sheets G-5 through G-163

These sheets provide descriptionsand testing procedures for the vavles and the 
rate of rise components.  You need the monometer boards to measure the rise of 
the mercury in the mercury checks and to ensure vacuum pressure in the sensing 
lines.

This isn't something you can find anymore - the components are no longer 
monufactured or sold by a company.  If someone has a manometer they want to 
sell - call me...   This isn't something your average inspector will know how 
to do. You have to find an elderly ex-Automatic guy.   These systems may have 
been installed with an electrical alarm but the valve is only tripped with the 
weight drop actuation caused by a rise in pressure behind the mercury check.

Actually, you can't even test per NFPA 25 in most cases.