Thank you, for your help.  I was able to speak with a technical
representative with Flamex and found out that their panel works just as you
described.  The burst of water is for 7 sec. or 13 gallons of water in the
small duct and 19.5 gallon in the large duct.

Matthew Stone
Unlimited Sprinkler Fire Protection
11130 Petal St.
Dallas, TX 75238

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Thursday, April 05, 2007 2:14 PM
To: [email protected]
Subject: RE: spark detection and extinguishing system

Matt,
The Flamex Panel says it can provide external alarms signals.  So take
an output from the flamex panel to the building main fire alarm panel as
an ALARM signal.  That way if the Flamex goes off it will be known.  Now
they may have this thing go off on a regular basis and that's just SOP,
in which case they may not want evacuation of the building and the fire
dept. dispatched every time it squirts.  If that's the case then just
make it a Supervisory alarm.

As far as indicating flow, Flamex has built-in flow monitors on their
system, if they are being provided, I'd use them and not a separate flow
switch.  Don't see an issue with tying it into your FP manifold below
your other system valves.  I would make sure to put a control valve on
the Flamex system with tamper tied into the fire alarm system.

You might need to check your hydraulics to make sure that if the flamex
discharges at the same time as one of the other systems, there will be
no performance degradation of either system.  But it appears that the
water usage for the flamex is minimal and in short bursts so that may
not be an issue.


Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to