Thom,

Indeed, in your area, the local water authority REQUIRES an RPZ on wet
systems (see Article 9, Mount Werner Water District).  I personally
object to RPZ being used inside and in pump rooms.  As you know,
virtually no contractor installs the recommended 2x ID RP drain
[primarily due to costs].  In certain failure modes the RPZ relief can
fully open [and stay open] impairing the fire sprinkler system, and in
my case, possibly flooding the fire pump room.  Further, RPZs are
indirectly responsible for "contaminating" anti-freeze loops - further
impairing systems in the winter.  Recognize that virtually all
suppression contractors use food grade additives, the use of the RPZ in
these situations is problematic. But, alas, we comply with the
applicable costs.

Byron
Freedom Fire
Longmont, CO

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] 
Sent: Sunday, April 22, 2007 11:00 AM
To: [email protected]
Subject: Sprinklerforum Digest, Vol 18, Issue 20

Send Sprinklerforum mailing list submissions to
        [email protected]

To subscribe or unsubscribe via the World Wide Web, visit
        http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
or, via email, send a message with subject or body 'help' to
        [EMAIL PROTECTED]

You can reach the person managing the list at
        [EMAIL PROTECTED]

When replying, please edit your Subject line so it is more specific
than "Re: Contents of Sprinklerforum digest..."


Today's Topics:

   1. Re: Sprinkler Drainage (Thom McMahon)


----------------------------------------------------------------------

Message: 1
Date: Sat, 21 Apr 2007 11:11:03 -0600
From: "Thom McMahon" <[EMAIL PROTECTED]>
Subject: Re: Sprinkler Drainage
To: <[email protected]>
Message-ID: <[EMAIL PROTECTED]>
Content-Type: text/plain; format=flowed; charset="iso-8859-1";
        reply-type=original

Actually there is no gray area that needs discussion.
The Fed. "Safe Drinking Water Act - 1986 Title XIV
Backflow prevention is required for all non-potable water connections to

potable water supplies.
Yes a wet sprinkler system is a non-potable water connection. (A low
hazard 
one and therefore able to be protected with a double check assembly.)
An antifreeze system or any system which has additative's present (Yes
that 
includes MIC treatment) is a high hazard system and requires a reduced 
pressure zone type backflow preventor.

In addition to the SDWA-1986 OSHA is also in on backflow requirements
for 
any workplace, with the Standards (29 CFR 1910) Subpart J 1910.141 a)
and 
b).

Then there are the additional requirements from individual states, which

each of you should become familiar with in those states where you
install 
systems. And finally the purveyor may have additional regulations for 
discharge of non-potable and waste water, as well as backflow
requirements 
that exceed the fed. or state requirements. Just be aware, that if a 
purveyor doesn't have a backflow prevention program in place that does
not 
mean you don't need to do it, it just means that you'll share the
liability 
if there is ever a problem.

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message ----- 
From: <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Friday, April 20, 2007 5:34 PM
Subject: Re: Sprinkler Drainage


>
> This issue was discussed briefly at the recent meeting of the NFSA
> Contractors Board.
> I have heard about the issue of treating sprinkler water as a
contaminant 
> in
> Southern California.
> I read the article you linked to, and don't think the author has a
clear
> understanding of the annual tests we perform on sprinkler systems. For

> example,
> he writes that Main Drain Test's are rarely conducted. In reality,
they're
> probably the most important part of an annual inspection.
>
> One issue to consider: If the system contains additives (ie
anti-freeze),
> then there may be cause for concern.
> What does the local water purveyor say? If he allows sprinkler systems
to 
> be
> connected without backflow devices (ie Detector Check Assembly), then
he 
> says
> the system is good enough to mix with his Water Supply.
>
> If he requires a Double Check Backflow, then he say's it's a "low
Hazard."
> (ie, it may smell bad, taste funny , etc)
>
> If he requires an RPZ Backflow, then he considers it high hazard
> contaminant. (These areas may be the ones that want sprinkler water 
> discharged  into
> sewers).
>
> I think the NFSA, AFSA and AWWA should jointly study this issue and
write 
> a
> paper to guide municipalities on this matter. Perhaps they have?
>
> Forest Wilson
> Cherokee Fire Protection Co.
> Dayton OH 45434
>
>
>
>
>
>
>
>
> In a message dated 4/17/2007 6:24:26 P.M. Eastern Daylight Time,
> [EMAIL PROTECTED] writes:
>
> ---  David Autry <[EMAIL PROTECTED]> wrote:
>
>> This article has  come to my attention. I'm just
>> wondering if anyone else has
>>  seen this. Anyone have any thoughts?
>>
>>
>>
>>
> http://www.plumbingengineer.com/april_07/designers.php
>>
>>
>>
>>
>>
>>
>>
>> David Autry
>>
>> Plans Examiner
>>
>> Nebraska  State Fire Marshal's Office
>>
>> 246 S. 14th Street
>>
>> Lincoln, NE 68508
>>
>> 402-471-9659
>>
>>  402-471-3118 fax
>>
>> www.sfm.ne.gov
>>
>>
>>
>
>
>
>
>
>
>
> ************************************** See what's free at 
> http://www.aol.com.
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email
to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
> 




------------------------------

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


End of Sprinklerforum Digest, Vol 18, Issue 20
**********************************************




_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to