One must assume that only 13 is identified in ASME A17.1 because it's the only one that REQUIRES sprinklers in these areas.

Roland

On Apr 23, 2007, at 11:15 AM, Kurt Olson wrote:

I have just the opposite problem. Condo building designed per 13R so no heads required in elevator but the elevator inspectors wishes to be the fire inspector and is requiring sprinklers in the pit and machine room. Problem is the elevator and machine room are basically detached from the
rest of the building separated by an out side walk way and there is no
way to install sprinklers without the potential for freezing. Inspector says that if there are sprinklers installed in the building the elevator
must have sprinklers per NFPA 13. When I try to explain that the
sprinklers are designed per NFPA 13R not 13 he says that ASME 17.1 only references NFPA 13 so he is not aware of 13R so sprinklers are required
per 13. Has anyone else had a similar problem?

Kurt Olson
East Coast Fire Protection

-----