Chris, et. al.

Please find the following; 

http://www.firesafety.gov/programs/alarms.shtm

http://www.firesafety.gov/downloads/pdf/white-paper-alarms.pdf

Sincerely,

John Drucker
Fire Protection Subcode Official (AHJ)
New Jersey


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Chris
Cahill
Sent: Friday, April 27, 2007 10:17 AM
To: [email protected]
Subject: RE: National Association of Home Builders is
orchestratingmajoropposition campaign against residential fire
sprinklers



Hopefully this comes through in tabular form.  What you are looking at
is the data that supports my earlier email.  It really jumps out if you
put it in graph form which is a limit of this forum.  This comes from
NFPA data.
And as you can see it goes back to 1977.  What happened between 1998 and
2007 I don't know but I don't have my hopes too high.

 

Now no one take this wrong, John, I and others are on the same side.  We
are at best debating some of the nuances of the same conclusion.  I
offer this information as I won't be in Rochester.  If some of you carry
forth more
information all the better.   

 

I agree John with your statements about smoke detectors back then not
being common.  But if I read your statement right "Lets not omit the
effect smoke alarms have had on residential life safety, their
implementation has cut the death rate in the vicinity of 50% from pre
smoke alarm period."  I think the data suggests otherwise.  

 

The death rates are nearly the same pre-smoke detectors and post smoke
detectors.  So I conclude smoke detectors aren't all they are cracked up
to be.  The rates are nearly the same based on "old codes vs. new
codes".  So I conclude codes haven't in themselves reduced the rate.
The total number of deaths have decreased by 50% but the total number of
fires have also decreased by 50%.  So I conclude the reduced number of
death is due nearly directly to the reduced number of fires.  Why has
the number of fires gone down?  It sure wasn't smoke detectors. 

 

Think about it the typical ionization detector while cheap doesn't do as
good a job with slow smoldering fires. As recent news special reports
suggest kids don't respond appropriately if at all to smoke detectors.
The young and old have much higher death rates.  Could this be related.
Smoke detectors don't help the impaired whether from self induced (beer
and the like), medical issues or old age.  I'm sure you, as I have, have
been to deaths with working smoke detectors.  I still have never met
anyone that has first hand experience in a sprinklered fire death.
Although Joe comes close as investigated one for FM. 

 

I believe we (the fire protection community) have put a 25 year trust
and reliance in the value of smoke detectors.  I believed the hype for a
time.
I repeated the slogans.  I now question smoke detectors as a failed
experiment.  When NAHB got up in '00 and said smoke detector were and
still are the answer I presented this data to challenge that assumption.
I hope
some one in Rochester does the same.    

 

 

 

Chris Cahill, P.E.

Fire Protection Engineer

Sentry Fire Protection, Inc.

 

763-658-4483

763-658-4921 fax

 

Email: [EMAIL PROTECTED]

 

Mail: P.O. Box 69

        Waverly, MN 55390

 

Location: 4439 Hwy 12 SW

              Waverly, MN 55390

 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of John
Drucker
Sent: Thursday, April 26, 2007 4:56 PM
To: [email protected]
Subject: RE: National Association of Home Builders is orchestrating
majoropposition campaign against residential fire sprinklers

 

Chris wrote; "On a per 1000 fires basis fires are just a deadly today as
25

years ago."

 

Chris with all due respect and admiration that would place the statistic
at

or around 1982 before hardwired interconnected smoke alarms one on each

level, outside sleeping areas and WITHIN EACH BEDROOM were required in
the

residential code, back then CABO . The latter was the key to early
warning

since prior to that detection and intimate warning within bedrooms was
never

required. In these "alarm protected" properties the survival rate is

significantly improved. Lets not omit the effect smoke alarms have had
on

residential life safety, their implementation has cut the death rate in
the

vicinity of 50% from pre smoke alarm period. Even the NAHB admits that
fact,

yet back in the day these same folks argued AGAINST smoke alarms. Lets
use

that same argument to promote sprinklers ! 

 

We still have that death gap where merely detecting a fire and alerting
the

occupants is not enough and that's the gap we intend to close with

residential one/two family homes and townhouse sprinkler requirements.

 

The NAHB will argue that that requring sprinklers in homes will not

eliminate the current 2,800 home fire deaths and on that note they are

correct. As noted earlier most fire deaths occur in older housing
outside

the reach of the IRC. But that's not the point !. IF WE DON'T START

SPRINKLERING NEW RESIDENTIAL CONSTRUCTION NOW IT WILL EVENTUALLY TURN
INTO

OLDER HOUSING AND THE CYCLE WILL CONTINUE.  

 

Start hiring fitters, we're gonna need them.

 

See you in Rochester !

 

Yours in Fire Safety

 

John Drucker

Fire Protection Subcode Official

New Jersey

 

 

 

-----Original Message-----

From: [EMAIL PROTECTED]

[mailto:[EMAIL PROTECTED] On Behalf Of Chris
Cahill

Sent: Thursday, April 26, 2007 2:22 PM

To: [email protected]

Subject: RE: National Association of Home Builders is orchestrating

majoropposition campaign against residential fire sprinklers

 

>From the NAHB: "The number of fatal fires has dropped dramatically in 
>the

last 20 years as the result of changes in residential construction

technology, improved building code requirements, consumer behavior and
the

concerted efforts of fire fighters, home builders and other safety

advocates. This trend continues and is all the more impressive given the

nation's growing population and housing stock."

 

This is just plain incorrect and the NAHB knows this as I debated it
with

them at the ICC hearing in '99-'01 when my proposal to sprinkler all R's
in

the IFC got passed.  The number of fatal fires are down but are down by
the

same rate as the total number of fires.  On a per 1000 fires basis fires
are

just a deadly today as 25 years ago.  Injuries are slightly up on a per
1000

fire basis.  I seem to recall the number is rather stable over time.
These

are researchable facts.  The other flaw in the NAHB thinking is all new

construction becomes old some day, just define old.  When they claimed

triumph in the 70's those new safe buildings are now the "old stock that
has

higher death rates".  Also, there is a strong tie to socioeconomic
factors.

The $350k houses of today will be occupied by the lower end as the upper
end

moves to the $1,000k in many years.  Now for my opinions (which as you
know

I don't often share hahahahaha).

 

The real improvements are we have less fires plain and simple.  Public

education has a role, but I think manufactures making their products
safer

has a bigger role.  Why are they safer - the legal system!  I think the

construction trades are doing better, particularly electrical.  Why -

research and codes and the legal system! I don't give much credit to the
IBC

or IFC, more exits, non-combustible construction, etc. IMHO don't reduce
the

number of fires.  But I will give you they might help the large multiple

loss fires like in the Station Fire R.I.  I'll also give you the numbers
are

skewed because nearly all the fatalities occur in residential which
really

don't have many safety requirements in the IBC or IFC.  Which is why

sprinkler and forget about it is the way to go.  I also don't give home

builders or general contractors too much credit.  Without insulting
them,

most really don't actually do anything.  They hire us and a variety of

others to actually build the thing.  And too many of them are just
looking

for the cheapest (and not necessarily code complaint) price.  

 

A leader in our State Fire Marshals Office once gave me a code change

proposal that replaced the entire empire of codes.  It went something
like

this:

 

Inspect building - Is it sprinklered? Yes, go to next building.

 

No - Issue order to sprinkler and schedule re-inspection.

 

Re-inspect - Is it sprinklered? Yes, go to next building.

 

No - Order it unsafe for human occupancy and schedule re-inspection.

 

Re-inspect - Is it sprinklered? Yes, go to next building.

 

No - Order it demolished and put on parking lot inspection list or I
guess

the green space improvement list.  

 

Now that's a life safety code!

 

Chris Cahill, P.E.

Fire Protection Engineer

Sentry Fire Protection, Inc.

 

763-658-4483

763-658-4921 fax

 

Email: [EMAIL PROTECTED]

 

Mail: P.O. Box 69

        Waverly, MN 55390

 

Location: 4439 Hwy 12 SW

              Waverly, MN 55390

-----Original Message-----

From: [EMAIL PROTECTED]

[mailto:[EMAIL PROTECTED] On Behalf Of John
Drucker

Sent: Wednesday, April 25, 2007 5:02 PM

To: [email protected]

Subject: RE: National Association of Home Builders is orchestrating
major

opposition campaign against residential fire sprinklers

 

 Fierce Fire Sprinkler Debate Expected at ICC Hearings  

 

April 23, 2007 - NAHB leaders are preparing for intense debate over

mandatory fire sprinklers during the International Code Council Final
Action

Hearings May 21-26 in Rochester, N.Y.

 

At issue is whether to move sprinkler requirements from the appendix
into

the main body of the 2006 International Residential Code, which governs

about 95% of new home construction. That move would make fire sprinkler

systems required in one- and two-family homes and townhouses.

 

NAHB is opposed to the amendment that would move the requirements, and
is

supported by many building officials who agree that code provisions

adequately provide for fire safety without needing mandatory sprinklers.

 

IRC amendments will be discussed May 22-23. The sprinkler amendment at
issue

is IRC proposal RB-114.

 

Proponents of fire sprinkler systems are encouraging their supporters to
go

to the hearings and sway the vote. They say sprinkler systems add an
average

of only $1.00 to $1.50 per square foot to the cost of a home.

 

However, an NAHB survey of installation costs in jurisdictions where

sprinklers are required demonstrates that the cost to builders can be as

high as $6.88 per square foot. Prices like that have a significant
impact on

housing affordability - preventing families who rent substandard housing

from purchasing a newer, safer home, NAHB has found.

 

A Smoke Alarms Work Web site was created by NAHB as a public safety tool
and

to remind home owners to maintain their smoke alarm systems. The site

includes helpful information about fire safety, as well:

 

The number of fatal fires has dropped dramatically in the last 20 years
as

the result of changes in residential construction technology, improved

building code requirements, consumer behavior and the concerted efforts
of

fire fighters, home builders and other safety advocates. This trend

continues and is all the more impressive given the nation's growing

population and housing stock.

 

 

>From 1979 to 2003, the rate of death from house fires dropped by more 
>than

58%, based on data from the Centers for Disease Control. That trend will

continue as more new housing stock is constructed and especially as home

owners are educated to maintain their smoke alarm systems.

 

 

U.S. Fire Administration and National Fire Protection Association data

continue to affirm that the vast majority of home fire fatalities occur
when

there are no operational smoke alarms. Based on a 2006 U.S. Fire

Administration study on the presence of working smoke alarms in
residential

fires, 88% of the fatal fires in single-family homes between 2001 and
2004

occurred where there were no working smoke alarms.

 

 

The same study shows that only 3.7% of residential fire deaths were
reported

as occurring in homes with working smoke alarms.

 

"The problem is not homes without sprinklers, the problem is homes
without

working smoke alarms," said Sandy Dunn, NAHB's first vice president.
"The

most proven, practical and affordable measure to preventing fire
fatalities

is ensuring that homes are equipped with smoke alarms and that they are

maintained."

 

If the sprinkler language remains in the appendix, the choice to mandate

sprinklers will be left to state and local jurisdictions - a choice ICC

officials said they preferred during the last code cycle.
"Unfortunately,

some of the very same sprinkler interests who advocated this position in
the

last cycle are now leading the charge to mandate sprinklers in the IRC,"

Dunn said.

 

"It is also unfortunate that they choose to expend so many resources to
push

for sprinkler mandates in homes that are already adequately protected by
IRC

requirements, especially when the overwhelming number of fire fatalities
are

occurring in homes without working smoke alarms," Dunn added.

 

NAHB is encouraging builders to communicate these concerns to local
building

officials and to encourage their attendance at the Rochester hearings to

vote against sprinkler mandates in the IRC. Members can also contact
their

local home builders association to find out how to help.

 

For more information, e-mail Jeff Inks at NAHB, or call him at
800-368-5242

x8547. 

 

 

 

_______________________________________________

Sprinklerforum mailing list

[email protected]

http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

 

To Unsubscribe, send an email
to:[EMAIL PROTECTED]

(Put the word unsubscribe in the subject field)

 

_______________________________________________

Sprinklerforum mailing list

[email protected]

http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

 

To Unsubscribe, send an email
to:[EMAIL PROTECTED]

(Put the word unsubscribe in the subject field)

 

_______________________________________________

Sprinklerforum mailing list

[email protected]

http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

 

To Unsubscribe, send an email
to:[EMAIL PROTECTED]

(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to