Many, many times.  It's always been the same manufacturer.  To their
credit, they've been pretty good about supplying checks with weaker
springs, as Tom mentioned.  Have the owner/contractor contact the local
rep.

Ed Kramer
Littlton, CO
>
>
>During waterflow alarm testing on a Wet Pipe NFPA-13 System I witnessed

>a phenomena wherein the vane type waterflow switch fluctuated back in 
>forth appx every 10 seconds making it impossible to set a 30 second 
>retard. Supply Pressure is 60 psi static, 55 psi Residual at 2" Main 
>Drain Test.  The WF Switch is mounted horizontally in a straight length

>of  6" Sch 10  48" from closest change in direction. Inspectors test is

>located downstream end of a branch line 1/2" orifice in place.
>
>The sprinkler contractor suspects theres a problem with this particular

>BFP. Anyone had a similar problem.
>
>Thanks
>
>John Drucker
>Fire Protection Subcode Official (AHJ)
>New Jersey


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to