within the existing building should not be a problem as long as access to
the room is from the exterior and not through a tenant space.

Garth

----- Original Message ----- 
From: "Todd Williams - work" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Friday, May 04, 2007 7:06 AM
Subject: Re: Single Fire Pump Serving Multiple Buildings


> Bobby,
>
> I've seen pumps servicing entire complexes quite a bit, so I don't
> see that as a problem. The issue about stand alone buildings vs.
> within an existing building could be a little bit of a gray area. You
> could have one tenant potentially controlling water supplies for a
> different tenant in another building. I would run this by the local
> AHJ and/or insurance carrier. The stand alone building would be the
safest.
>
>
> At 07:47 AM 5/4/2007, you wrote:
> >Is there something in the IFC or IBC 2006 or NFPA 20 which would
> >prohibit a booster fire pump from supplying multiple buildings on the
> >same property?  Would it make any difference if the fire pump was in a
> >stand alone building or inside a two hour enclosure of one of the
> >protected buildings?
> >
> >The scenario is a developer with three detached 200K sq ft spec
> >warehouse buildings with ESFR systems, all on one property, a good
> >public water supply but not quite good enough.  All buildings are
> >supplied from a single tap to the public water system with a DDC device
> >in a vault.
> >
> >NFPA 13-07 8.2.5 refers to "systems" or "risers" and I don't see the
> >intent for it to include a booster pump supply.
> >
> >Bobby McCullough
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >To Unsubscribe, send an email to:[EMAIL PROTECTED]
> >(Put the word unsubscribe in the subject field)
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, Connecticut
> 860-535-2080
> www.fpdc.com
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to