Years ago when the Star Dry Pendent issue was relatively young, I recall
meeting with the Owner of a private nursing home. He asked if the law
required him to change them out, and I replied I knew of none. That ended
the discussion. 

Was I legally, morally, or ethically bound to then call the local AHJ?
And if this was a Vrp (accent on Voluntary) replacement (and pardon me, I
don't recall if the Star DP was voluntary or not) would I have the same
obligation? I'm leading back to Thom's below note, what could the AHJ then
do, absent a local amendment to enforce something the CPSC didn't do? 

BTW, I am curious if anyone is aware of legal cases where a contractor was
guilty of NOT informing an AHJ, absent a legal requirement such as GA now
has? 

George Church
Rowe Sprinkler

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom McMahon
Sent: Friday, May 04, 2007 10:57 AM
To: [email protected]
Subject: Re: Article on Sprinkler Recall

Just to ADD to what George is saying here. You all do remember that this is 
a voluntary Recall? Voluntary by both the property owner and the 
Manufacturer. Unless your state has passed a specific ordinance requiring 
the replacement of these heads by a specific date, your state has accepted 
an "Unsafe" condition to exist without and specific time for correction, 
which makes them complacent or a Co-Defendant.

The law has no requirement of notification of a voluntary compliance issue.

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message ----- 
From: "George Church" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Friday, May 04, 2007 8:51 AM
Subject: RE: Article on Sprinkler Recall


> Could you also be sued by a property owner by calling in enforcement when
> you're not legally obligated to?
>
> glc
>
> Drucker
> Sent: Friday, May 04, 2007 7:38 AM
> To: [email protected]
> Subject: RE: Article on Sprinkler Recall
>
> But lets face it a letter to the government AHJ does more then simply
> "notify someone". This notification unlike any other will result in the
> "responsible" party being compelled to resolve the issue, which mitigates
> the hazard, which reduces the chance of litigation, which protects 
> property,
> which saves lives !
>
> Check with your attorney ask him/her if that makes sense, ask him/her if a
> reasonable person would consider it prudent to notify the authority of
> jurisdiction responsible for public safety whenever a condition arose that
> cou


ld endanger that safety.
>
> If uncommon sense doesn't compel someone we have the Fire Codes reporting
> and notification requirements and the legal doctrines of ones duty of care
> and duty to act.
>
> Yours in Fire Safety
>
> John Drucker
>
>
> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Todd 
> Williams
> - work
> Sent: Thursday, May 03, 2007 11:29 PM
> To: [email protected]
> Subject: RE: Article on Sprinkler Recall
>
> George,
>
> I would think that any professional, be it contractor, designer or
> whatever, who does not notify someone,(I opt for the owner, because
> they have a certain responsibility) of a dangerous condition they are
> aware of, could bear some responsibility if that condition leads to a
> loss. It may be criminal or civil, but the issue remains. I tend to
> equate them because they both involve something I don't like to
> do....give lawyers money. A letter to a building owner, which should
> take no more than 10 minutes to write, could save a lot of headaches
> down the road. Well worth the investment, IMHO.
>
>
> At 12:45 PM 5/3/2007, you wrote:
>>While I'll certainly agree it's the right thing to do, I vehemently
> disagree
>>that the sprinkler industry- at least we dumb installing contractors- have
> a
>>legal or fiduciary duty to contact a fire official.
>>
>>I believe there is a higher standard for registered design professionals;
>>but we work for the building owner in many cases, but we are in no way,
>>shape or form obligated by any law I'm aware of to act as an enforcement
>>entity, or snitch.
>>
>>That's NOT to say that a widow's lawyer wouldn't drag us in and state that
>>we should have recognized a clear and present danger, and taken action- I
>>just never heard of any legal requirement.
>>
>>Has anyone else heard of such a requirement, or case law (outside Calif)
>>where a contractor was liable for not contacting an enforcement agency?
>>
>>Can you imagine an auto mechanic being charged with contributing to
>>manslaughter if someone drove in, asked him to check their brakes, he
>>discovers they are defective, the car owner refuses to allow him to fix
>>them, and drives off- and the mechanic doesn't call the police and give
>>licenses number, let alone follow in pursuit so as to be able to guide the
>>police to the "escaping" vehicle? If this were the case, there would be
>>standards requiring mechanics be located in areas with cel reception, have
>>cel phones with charged batteries at the ready, and a pursuit vehicle
> parked
>>so as to allow ready exit to pursue.
>>
>>Anyone aware of a parallel in sprinkler contracting?
>>
>>George Church
>>Rowe Sprinkler
>>
>>-----Original Message-----
>>From: [EMAIL PROTECTED]
>>[mailto:[EMAIL PROTECTED] On Behalf Of John 
>>Drucker
>>Sent: Thursday, May 03, 2007 11:23 AM
>>To: [email protected]
>>Subject: RE: Article on Sprinkler Recall
>>
>>Todd,
>>
>>Its really quite simple. Notify your local fire official (AHJ) in
>>writing of any known fire sprinkler systems where the replacement of
>>sprinkler heads effected by the recall has not been accomplished. The
>>sprinkler industry has a duty of care and fire officials have a duty to
>>act.
>>
>>Besides all that it's the right thing to do. The last thing the
>>sprinkler industry needs is a fire loss due to defective product where
>>the integrity of the industry and fire sprinkler systems in general is
>>brought into question. Lets seize this opportunity before it slips away.
>>
>>Yours in fire safety
>>
>>John Drucker
>>
>>
>>-----Original Message-----
>>From: [EMAIL PROTECTED]
>>[mailto:[EMAIL PROTECTED] On Behalf Of Todd
>>Williams - work
>>Sent: Wednesday, May 02, 2007 8:27 PM
>>To: [email protected]
>>Subject: RE: Article on Sprinkler Recall
>>
>>I think it's incumbent on everyone to notify a building owner of the
>>presence of sprinklers under recall. However, the "failing to take such
>>action to remedy" almost sounds like we all have to carry boxes of
>>replacement sprinklers wherever we go and change any recalled heads we
>>see. As an Engineer, I would think my responsibility would be to notify
>>the proper entities (owners, franchisers, etc) of the condition and then
>>it is up to them to remedy. I have done this in the past in a hotel I
>>was staying in and the sprinklers were changed.
>>The criminal offense would (or should) be an owner knowingly allowing a
>>dangerous condition to exist. If, as John states, having knowledge of
>>such a condition and failing to take action (beyond notification) is a
>>criminal offence, then I'm turning in my PE and getting a Snapple route.
>>
>>
>>At 06:53 PM 5/2/2007, you wrote:
>> >Or the AHJ's.  Having knowledge of a condition which may jeopardize the
>>
>> >health safety and welfare of persons including firefighters and failing
>>
>> >to take such action to remedy such conditions in a timely manner which
>> >ultimately results in an injury or death is a criminal offense.  Tyco,
>> >likewise sprinkler contractors, should in their own interest turn over
>> >such records to the proper authorities so that enforcement action can
>> >be commenced.
>> >
>> >John Drucker
>> >Fire Protection Subcode Official (AHJ)
>> >Borough of Red Bank, NJ
>> >
>> >-----Original Message-----
>> >From: [EMAIL PROTECTED]
>> >[mailto:[EMAIL PROTECTED] On Behalf Of
>> >[EMAIL PROTECTED]
>> >Sent: Wednesday, May 02, 2007 3:59 PM
>> >To: [email protected]
>> >Subject: RE: Article on Sprinkler Recall
>> >
>> >While working for TYCO it was surprising how many owners who knew about
>>
>> >the recall would put us off and reschedule and reschedule their change
>> >outs.  It wasn't convenient and they just didn't want to fool with it.
>> >Even though they knew the risk.  I can totally see why TYCO would want
>> >to see an end to it.  If owners hadn't scheduled their replacement by
>> >now they either don't care, can't schedule a convenient time, or have
>> >not had their systems inspected properly for years so they don't know
>> >what they have.  We had plenty of people call us for inspections when
>> >the news first came out, just to make sure they didn't have the
>> >sprinklers installed.  But then the concern for the matter waned.
>> >Convenience was probably the biggest reason for not getting it done.
>> >I'd hate to be the owner who knew about it and didn't get it done and
>> >then have a fire incident.  I wonder what the insurance companies would
>> >say about that, let alone the lawyers.    Oi Vey!
>> >
>> >
>> >
>> >Craig L. Prahl, CET
>> >Fire Protection Group
>> >Mechanical Department
>> >CH2MHILL
>> >Lockwood Greene
>> >1500 International Drive
>> >PO Box 491, Spartanburg, SC  29304-0491 Direct - 864.599.4102 Fax -
>> >864.599.8439 [EMAIL PROTECTED] http://www.lg.com
>> >
>> >
>> >-----Original Message-----
>> >From: [EMAIL PROTECTED]
>> >[mailto:[EMAIL PROTECTED] On Behalf Of Rod
>> >DiBona
>> >Sent: Wednesday, May 02, 2007 3:02 PM
>> >To: [email protected]
>> >Subject: RE: Article on Sprinkler Recall
>> >
>> >Thanks George,
>> >
>> >I can sympathize with Tyco not wanting this thing to drag on
>>indefinitly
>> >but the fact is that this could be very bad for our industry.
>>Inevitably
>> >there will be more sprinklers with potential problems left in place
>> >because of this decision and at the end of the day a higher percentage
>> >of possible failures. In the long run I don't believe that this puts
>>any
>> >of us in a better situation....including Tyco.
>> >
>> >Rod DiBona
>> >Rapid Fire
>> >
>> >-----Original Message-----
>> >From: [EMAIL PROTECTED]
>> >[mailto:[EMAIL PROTECTED] On Behalf Of George
>> >Church
>> >Sent: Wednesday, May 02, 2007 10:24 AM
>> >To: [email protected]
>> >Subject: RE: Article on Sprinkler Recall
>> >
>> >Recalling a Recall
>> >Federal Agency Ends Callback
>> >Of Faulty Fire Sprinklers
>> >In First-Ever Reversal
>> >By CHRISTOPHER CONKEY
>> >May 1, 2007; Page D1
>> >
>> >Almost every day, the Consumer Product Safety Commission initiates a
>> >recall of a snowmobile, battery or other product seen as a safety
>> >hazard. Today, it will announce for the first time that it is doing
>>just
>> >the opposite: ending a recall despite millions of faulty units still in
>> >use.
>> >
>> >
>> >In 2001, following reports that some fire sprinklers made by Central
>> >Sprinkler Co. failed to work during fires, the CPSC negotiated a
>>massive
>> >recall of 35 million sprinkler heads used in apartments, schools,
>> >hospitals and other commercial buildings. New Jersey-based Tyco
>> >International, which acquired Central Sprinkler, agreed to pay for
>> >replacement parts and the labor to install them.
>> >
>> >Many of the bad sprinkler heads have since been replaced, and Tyco says
>> >it may spend $500 million on the effort, likely making it the most
>> >expensive recall in CPSC history. But there are still roughly 13
>>million
>> >potentially dangerous units in use, either because building managers
>> >don't know about the recall or haven't yet taken action. Now, the
>>agency
>> >says it will end the sprinkler recall in four months, hoping that the
>> >finality of a deadline and one last wave of publicity will prod the
>> >remainder to sign up.
>> >
>> >The decision, which will relieve Tyco of having to pay for replacements
>> >and labor if building managers don't apply by the Aug. 31 deadline, is
>>a
>> >bit of an experiment by the CPSC, and it shows how the agency is
>> >wrestling with some tough questions: How can it make recalls more
>> >effective, and will more people take advantage of recalls if the time
>> >period for doing so is shortened?
>> >
>> >Recalls, such as a recent one concerning tainted pet food, are
>> >occasionally big news, but most come and go with little notice by
>> >consumers. For some time, the CPSC, which examines the broadest
>>spectrum
>> >of consumer products that aren't food, drugs or cars, has been
>> >struggling to find ways to change that.
>> >
>> >In 2003, the three-member commission considered a petition from safety
>> >advocates that would have required manufacturers to include
>> >contact-information cards with products, enabling them to directly
>> >notify some consumers of a recall. The proposal was similar to one long
>> >mandated for makers of child safety seats by the National Highway
>> >Traffic Safety Administration. That requirement, a 2002 NHTSA study
>> >found, resulted in higher product-registration and recall-participation
>> >rates.
>> >
>> >Ultimately, two CPSC commissioners voted against the
>>contact-information
>> >card proposal on the grounds that it was vague, costly and unlikely to
>> >have a major impact; another commissioner essentially voted for the
>> >petition because he felt the issue deserved more attention. At the
>>time,
>> >CPSC Chairman Hal Stratton, who voted against the proposal, said a
>> >"comprehensive" review of recall effectiveness was under way and a
>>major
>> >study would be concluded in 2004.
>> >
>> >Yesterday, CPSC spokeswoman Julie Vallese said that the review cited by
>> >Mr.
>> >Stratton, who left the agency last year, is continuing and the
>> >commission is exploring ways to use technology to improve outreach to
>> >consumers. She cited a recent CPSC move to allow consumers to receive
>> >email notices when products they care about are recalled. "The agency
>>is
>> >always trying to find new and effective ways to reach out to
>>consumers,"
>> >she says.
>> >
>> >In the sprinkler case, the agency's decision to grant Tyco's request to
>> >end the recall represents a calculated gamble that more building
>> >managers will hear about the recall and act on it sooner if a deadline
>> >is in place than if the program were to continue indefinitely. Many
>> >superintendents inspected their sprinklers and signed up for the recall
>> >in the two years after it was announced, but the pace has slowed in
>> >recent years.
>> >
>> >"Whoever hasn't participated, we want them to act now," says Howard
>> >Tarnoff, the CPSC attorney who is handling the sprinkler case. "We
>>think
>> >there's going to be a surge."
>> >
>> >Tyco thinks this is a good way to proceed, too. "Because of the pattern
>> >of responses having dropped off ... we want to give one final push,"
>> >says Anne Buchanan, a spokeswoman for Tyco Fire & Building Products.
>>"We
>> >encourage all building and homeowners to check to see if they have
>>these
>> >affected sprinklers and are eligible for free replacement."
>> >
>> >
>> >But the CPSC's decision also carries the risk that some building
>> >managers won't hear about the recall or take action by the deadline. It
>> >will also test the ability of fire marshals, distributors and others
>> >involved in identifying sprinkler systems that need to be replaced.
>> >
>> >Washington state's fire marshal office has been particularly aggressive
>> >in its efforts to get faulty systems changed out. The office secured
>> >money to pay for two deputy fire marshals to scour the state looking
>>for
>> >buildings still using the problematic systems. So far, according to
>> >Anjela Foster, assistant state fire marshal, they have located 800,000
>> >sprinkler heads in need of replacement.
>> >
>> >But that's only "pretty close to the halfway point," Ms. Foster says.
>> >She estimates there are roughly two million defective sprinklers in
>>need
>> >of replacement and it will take five years to get them all replaced.
>>"If
>> >the recall ended, the effect to us would obviously be people wouldn't
>>be
>> >able to turn in claims," she says. "We would like to have enough time
>>to
>> >get into the remaining facilities."
>> >
>> >_______________________________________________
>> >Sprinklerforum mailing list
>> >[email protected]
>> >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>> >
>> >To Unsubscribe, send an email
>> >to:[EMAIL PROTECTED]
>> >(Put the word unsubscribe in the subject field)
>> >_______________________________________________
>> >Sprinklerforum mailing list
>> >[email protected]
>> >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>> >
>> >To Unsubscribe, send an email
>> >to:[EMAIL PROTECTED]
>> >(Put the word unsubscribe in the subject field)
>> >_______________________________________________
>> >Sprinklerforum mailing list
>> >[email protected]
>> >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>> >
>> >To Unsubscribe, send an email
>>to:[EMAIL PROTECTED]
>> >(Put the word unsubscribe in the subject field)
>> >
>> >_______________________________________________
>> >Sprinklerforum mailing list
>> >[email protected]
>> >http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>> >
>> >To Unsubscribe, send an email
>>to:[EMAIL PROTECTED]
>> >(Put the word unsubscribe in the subject field)
>>
>>Todd G. Williams, PE
>>Fire Protection Design/Consulting
>>Stonington, Connecticut
>>860-535-2080
>>www.fpdc.com
>>
>>_______________________________________________
>>Sprinklerforum mailing list
>>[email protected]
>>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>>To Unsubscribe, send an email
>>to:[EMAIL PROTECTED]
>>(Put the word unsubscribe in the subject field)
>>
>>
>>_______________________________________________
>>Sprinklerforum mailing list
>>[email protected]
>>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>>To Unsubscribe, send an email to:[EMAIL PROTECTED]
>>(Put the word unsubscribe in the subject field)
>>
>>_______________________________________________
>>Sprinklerforum mailing list
>>[email protected]
>>http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>>To Unsubscribe, send an email to:[EMAIL PROTECTED]
>>(Put the word unsubscribe in the subject field)
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, Connecticut
> 860-535-2080
> www.fpdc.com
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
> 


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to