Hello Tony,

Thankie Sir...   This little ole apprentice designer stumper
my NICET IV when I mentioned this to him and he wanted to see it
himself.

Friday, May 4, 2007, 2:16:56 PM, you wrote:

> Charles,

> NFPA 13 (2002)  8.3.5 Thread Size Limitations

> Tony Liddic, CET
> Fire Sprinkler Designer
> AEC Fire & Security
> 400 Fame Rd.
> West Carrollton, OH  45449
> 937-866-4158
> 937-865-0212 fax
> [EMAIL PROTECTED]

> -----Original Message-----
> From: [EMAIL PROTECTED]
> [mailto:[EMAIL PROTECTED] On Behalf Of Charles
> Thurston
> Sent: Friday, May 04, 2007 2:12 PM
> To: Greg McGahan
> Subject: Re: 1/2" thread - 8 K sprinklers

> Hello Greg,



> Wednesday, April 25, 2007, 12:19:42 PM, you wrote:

>> NFPA 13 clearly states that we can not use 8.0 k heads with 1/2" threads
> in
>> new installations. I assume there are reasons for this but I do not know
>> them.

> Does anybody have the chapter and verse where it states this handy ? I
> can not find it.



>> BUT, we have a new job with pipe on the floor and 1/2" welded outlets for
>> 5.6 k sprinklers. The problem is we ran into some lights and are having to
>> move some pipe which blows our calcs. (Our designer made a mistake and did
>> not realize that the lights are not hanging, but are mounted to the
>> purlins.)

>> We had in excess of 10% cushion and now we have -5%. If we use the 8K
> heads
>> we are fine. 

>> The other option is to reorder all of the branchline piping 1 size larger.

>> We reflowed the hydrants to confirm the water and lost 10 psi residual to
>> make matters worse.

>> Does anyone on the committee have any input before I ask the AHJ to
> consider
>> this change? 

>> Greg

>> Living Water Fire Protection, LLC
>> 1160 McKenzie Road
>> Cantonment, FL 32533
>> 850-937-1850
>> Fax: 850-937-1852



>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

>> To Unsubscribe, send an email
>> to:[EMAIL PROTECTED]
>> (Put the word unsubscribe in the subject field)





-- 
Best regards,
 Charles                            mailto:[EMAIL PROTECTED]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to