Yes! It's the same 12 Ga. wire that is used to suspend the ceiling grid. Ask your ceiling guy where to get it. Usually comes in 10' 15' and 20' lengths.

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message ----- From: "Charles Thurston" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Tuesday, May 29, 2007 9:18 AM
Subject: Branch Line Restraint


Hello sprinklerforum,

 NFPA Allows 12 gauge wire to be used as restraint per 9.3.6. Looking
 in the Annex for this section it shows wire twisted back onto itself
 as a method of securing it to the structure. All I have been able to
 find in "aircraft" type cable. Does anyone know of a solid wire that
 can be used like the annex shows?

 Thanks

--
Best regards,
Charles                          mailto:[EMAIL PROTECTED]
Coastal Fire Protection