Yes! It's the same 12 Ga. wire that is used to suspend the ceiling grid. Ask
your ceiling guy where to get it. Usually comes in 10' 15' and 20' lengths.
Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message -----
From: "Charles Thurston" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Tuesday, May 29, 2007 9:18 AM
Subject: Branch Line Restraint
Hello sprinklerforum,
NFPA Allows 12 gauge wire to be used as restraint per 9.3.6. Looking
in the Annex for this section it shows wire twisted back onto itself
as a method of securing it to the structure. All I have been able to
find in "aircraft" type cable. Does anyone know of a solid wire that
can be used like the annex shows?
Thanks
--
Best regards,
Charles mailto:[EMAIL PROTECTED]