In my 1983 edition the requirement is listed and there is a bar next to
the section indicating that it was either new or changed.  But, there
are other references to the check valve that don't indicate changes, so
the requirement definitely predates 1983.  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Sean &
Christine Conlin
Sent: Thursday, May 31, 2007 9:44 AM
To: [email protected]
Subject: FDC check valves

Good day to all!
   
  Does anyone know when NFPA 14 or other NFPA standard first initiated
the requirement for a check valve in the fire department connection?
   
  Thanks for the help in advance.
   
  Sean