Greg,

>From NEC (2005) Article 695 Fire Pumps 

695.1(B) Not Covered. This Article does not cover the following:

(2) Pressure maintenance (jockey or makeup) pumps.

However, Article 696 does provide the following with regards to when
"other loads" are connected (although not required to be) to the fire
pump feed.

695.5 Transformers

695.5(C) Feeder Source 

Where a feeder source is provided in accordance with 695.3(B)(2),
transformers supply fire pump system shall be permitted to supply other
loads. All loads shall be calculated in accordance with Article 220,
inlcuding demand factors as applicable.

Conductor sizing is also addressed at 695.6(C)(1)

The section of NFPA-20 you cited only refers to the fire pump
controller.

Hope that helps

John Drucker
Fire Protection Subcode Official (AHJ)
Licensed Electrical Contractor 
New Jersey

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg
McGahan
Sent: Friday, June 15, 2007 10:11 AM
To: [email protected]
Subject: jockey pump power

An electrician informed me this morning that the NEC requires him to
size his electrical feed for the fire pump and the jockey pump.

NFPA #20 states the following: 
10.3.4.8 Electrical supply conductors for pressure maintenance (jockey
or
make-up) pump(s) shall not be connected to the fire pump controller.

We are not electricians nor did we stay in a Holiday Inn Express last
night; but he wants to know where he is supposed to get his power from
for the Jockey Pump. Can he come off the feed from the transformer prior
to entering the Fire Pump Control Panel?

Greg

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to