Joe,

I agree with your reasoning and will be removing the foam but, I don't
believe that your response reflects what is now written in NFPA 13.
Below is the proposal from the ROP for the referenced section.  

Looking at the substantiation, the submitter was trying to come up with
language so that the user or enforcer could determine whether or not the
material will propagate fire.  

The way I read it, there is no reference to a corner test in any way.
The only test is the NFPA 255 test that appears to have been mistakenly
extended for 20 minutes.  Unless I am mistaken, I don't believe that
anyone could use this section comfortably to allow any material since
there is no published documentation that the NFPA 255(E84) test has been
extended for 20 minutes and shows a material "not to propagate fire."
There isn't any criteria in that standard to come to that conclusion.

Actually, the foam that I have data on would give a 25 or less rating
flame spread on all surfaces just as the fire retardant treated wood as
indicated by the submitter of the proposal, but I don't know that either
would be shown "not to propagate fire" so as to meet this section. Maybe
if the other test were referenced (NFPA 286) the section would make more
sense?

Thanks

Peter
 

13-293 Log #823 AUT-SSI Final Action: Accept in Principle
(8.14.2.10)
_______________________________________________________________
SUBMITTER: Joseph T. Holland, III, Hoover Treated Wood Products
RECOMMENDATION: Revise text to read as follows:
8.14.1.2.10 Concealed spaces where rigid materials are used and the
exposed
surfaces have a flame spread rating of 25 or less ,[new]a smoke
developed rating of
50 or less,[new] and the materials have been demonstrated not to
propagate fire
[new]when tested in accordance with NFPA 255, Standard Method of Test of
Surface
Burning Characteristics of Building Materials, 2000 edition, extended
for an
additional 20 minutes [new] in the form in which they are installed
shall not require
sprinkler protection.
SUBSTANTIATION: The section as written does not tell the user or
enforcer
how to determine whether or not the material will propagate fire or how
long it
needs to be exposed to fire to make that determination. The section as
written
could allow a brush-on or paint-on coating to be used. The proposal
establishes
a test method and a duration of time for exposure. The requirements are
similar
to fire-retardant-treated wood. FRTW is allowed in 8.14.1.2.11.
Materials
approved under 8.14.2.10 should be at least equivalent to FRTW. Smoke is
an
important factor in a fire in that too much can hinder escape, rescue
and fire
fighting.
COMMITTEE MEETING ACTION: Accept in Principle
Accept in principle, change to read:
8.14.1.2.10 Concealed spaces where rigid materials are used and the
exposed
surfaces have a flame spread index of 25 or less , and the materials
have been
demonstrated not to propagate fire [new]when tested in accordance with
NFPA 255,
Standard Method of Test of Surface Burning Characteristics of Building
Materials, 2000 edition,[new] extended for an additional 20 minutes in
the form in
which they are installed shall not require sprinkler protection.
COMMITTEE STATEMENT: Submitter presented to the committee his
comments and agreed with the changes made to the proposal. The committee
felt that the comments about smoke ratings would be of no use in the
standard
and would just lead to confusion.
NUMBER ELIGIBLE TO VOTE: 30
BALLOT RESULTS: Affirmative: 29
BALLOT NOT RETURNED: 1 AMAR
  


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Joe
Hankins
Sent: Monday, June 18, 2007 5:44 PM
To: [email protected]
Subject: Re: Non-combustible concealed space - or is it?

Peter,

As the E84 test is a horizontal burning test and your insulation is 
installed on walls, the E84 test does not meet the "in the form they 
which they are installed" criteria.

More importantly, corner tests have shown repeatedly that exposed foam 
with 25  flame spread can produce a spectacular fire when installed on 
walls..  In fact, 25 flame spread insulation on walls can produce a fire

that will race ahead of sprinklers, stopping only when it runs out of 
foam to burn..  Exposed foam on walls is bad news, with or without 
sprinklers.

Joe


Larrimer, Peter A wrote:
> NFPA 13 states the following.
>
> 8.15.1.2.10  Concealed spaces where rigid materials are used and the
> exposed surfaces have a flame spread index of 25 or less, and the
> materials have been demonstrated not to propagate fire when tested in
> accordance with NFPA 255, Standard Method of Test of Surface Burning
> Characteristics of Building Materials, extended for an additional 20
> minutes in the form in which they are installed, shall not require
> sprinkler protection.
>
> I have a foam insulation sprayed on the walls of an otherwise
> non-combustible concealed space, that has a 25 or less flame spread
that
> is marketed as flame retardant in accordance with ASTM E84 (same as
the
> NFPA 255 test). 
>
> Can anyone educate me on what  "and the materials have been
demonstrated
> not to propagate fire when tested in accordance with NFPA 255,
Standard
> Method of Test of Surface Burning Characteristics of Building
Materials,
> extended for an additional 20 minutes in the form in which they are
> installed" means?  
>
> Considering that the tunnel test measures materials installed on the
> tunnel ceiling so I am not sure what this code language means.  Can
> anyone shed some light/committee members?
>
> Would you accept the material in a non-combustible concealed space?
>
> Thanks
>
> Peter A. Larrimer PE
> Safety & Fire Protection Engineer
> VISN 4
> Voice 412-365-5466
> Cell 412-999-1321
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> To Unsubscribe, send an email
to:[EMAIL PROTECTED]
> (Put the word unsubscribe in the subject field)
>
>   

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to