No, however it must comply with the applicable requirements of 2005 NEC 695.6(A) for line side (service) conductors and 2005 NEC 695.6(B) for load side (supply) conductors.
John Drucker Fire Protection Subcode Official Licensed Electrical Contractor New Jersey -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Thomas Reinhardt Sent: Wednesday, June 20, 2007 4:25 PM To: [email protected] Subject: Power source for electric fire pump Does the electric power source for a fire pump need to be encased in concrete? Thanks Tom _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)