What would be your justification for not protecting that room?  I can
not find anything that would permit omission of sprinklers.  

Paul J. Pinigis, P.E.
Chief Life Safety Engineer

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Karen
Purvis
Sent: Friday, June 22, 2007 1:44 PM
To: [email protected]
Subject: RE: Steam Room

But the question still is; is there somewhere in the code that states
that
this is how you treat a steamroom. In other words do I have to have that
area covered?


Karen Purvis
Designer
Facility Systems Consultants
714 S Gay St
Knoxville, TN 37902
ph.865-246-0164
fax 865-246-1084

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Thom
McMahon
Sent: Friday, June 22, 2007 1:32 PM
To: [email protected]
Subject: Re: Steam Room

Actually we use 360'F heads in our sauna's and 286 in steam rooms. Steam
is 
212'F max unless its under pressure, (at a pressure above atmospheric)
which

should never occur in a steam room. The sauna is higher because the 
electrical cut out is usually well over 200'F (As high as 300). We
protect 
both as light haz.. even tho the sauna has un-treated wood thru out, can

have more in the way of combustible lotions oils and towels in contact
with 
the dry heat element, than is usually able to happen in the
non-combustible 
steam room.

Thom McMahon
Firetech, Inc.
2560 Copper Ridge Dr
Steamboat Springs, CO 80488-2136
Tel: 970-879-7952
Fax: 970-879-7926
----- Original Message ----- 
From: "Jamie Seidl" <[EMAIL PROTECTED]>
To: <[email protected]>
Sent: Friday, June 22, 2007 11:24 AM
Subject: RE: Steam Room


I talked with a sauna rep awhile back on this same issue.  They
recommend a 286 deg head.


Jamie Seidl



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to