If the building is sprinkled you can have up to 26,400 gallons in the
building for Class IIIB.  That's spelled out in the IBC, see Table
307.7(1).

Tank construction material is not restricted also as long as the
building is sprinkled.  NFPA 30, 4.2.2.  Although in some cases you may
be asked to increase the density and remote area if the tank is plastic
or any similar combustible composition.  Check with your AHJ and/or
Underwriter.

You also need to know what else is being stored near that tank.  If
there are Class I or II flammables then there are relief venting
requirements.

Also you might walk through the decision tree in NFPA 30, Chapter 6.8
and see where your IIIB fits.  That tree can help when there is some
question how to protect the area and it's not printed in black and
white.

And by all means, get an MSDS on the stuff.




Craig L. Prahl, CET
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.lg.com


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Todd
Williams - work
Sent: Friday, June 29, 2007 5:19 PM
To: [email protected]
Subject: Indoor tank storage

Any ideas for indoor 5000 gallon tank storage of Class IIIB flammable
liquids? NFPA 30 is silent on this.

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, Connecticut
860-535-2080
www.fpdc.com 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to