The maintenance can really be a pain too. For instance, if the
concentration is a little low, you have to drain the entire system,
modified the captured solution (or replace it), then pump it back
into the system. That can be interesting on a 500 gallon system.
NFPA 25 has historically been too vague on this aspect but that will
be clarified in the 07 ed being released soon (around Sept).
Roland
On Jul 5, 2007, at 7:13 AM, Rod DiBona wrote:
In my opinion this is a really bad idea. Been there and done that and
the dry system is the better choice here by far. If I were you I would
sit down with them and educate them on all of the issues that you have
just addressed with the antifreeze and I WOULD definitely tell them of
the approximate replacement cost. What does the antifreeze have to do
with if it was 13 or 13R? What is the water source if the
underground is
to be filled w/ af. Remember this must be glycerin if it is going
to be
cpvc. Was the 10 yr old system galvanized?
Rod DiBona
Rapid Fire
-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Coastal
Sent: Tuesday, July 03, 2007 7:43 PM
To: [email protected]
Subject: Unusual Situation
Hello sprinklerforum,
I am open to suggestions on this one.
We have a customer in a 4 story residential building wanting to
replace the entire system due to rusted/leaking pipes in the old
system.
They are requiring the system to be installed with CPVC piping.
They are requiring the ENTIRE system to be filled with
Anti-Freeze including the underground.
They are wanting to put the DCDA Backflow, Then the Alarm Valve,
Then the RPZ Backflow and Expansion Tank into a hotbox outside.
To me it looks like the use of Anti-Freeze bumps it to a 13
system instead of 13R. The new piping is to be built into new
soffits on
the outside of the building walkways. They have a Dry Pipe system now
and do not want the leaking problems they have now to recur in a few
years like the existing 10 year old system. I am not even bring up the
subject of Anti-Freeze recovery/reuse when the system is tested or
when
the Alarm company does a flow to test the WF switches quarterly. The
Main Drain flow test is another subject...
--
Best regards,
Charles Thurston
Coastal Fire Protection
mailto:[EMAIL PROTECTED]
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:Sprinklerforum-
[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)