Doug, To properly size the air compressor, you would multiply the dry system volume by .012 This converts the capacity (in gallons) to cubic feet per minute of free air capacity.
This calculation should give you the proper amount of air capacity needed to re-charge your dry system to 40 psi in 30 minutes. Ray Vance Chief Engineering Tech. Wayne automatic Fire Sprinklers, Inc. (407) 656-3030 www.waynefire.com -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of douglas hicks Sent: Saturday, July 21, 2007 9:14 PM To: sprinkler board Subject: Air Compressor for dry system How do I size an air compressor for a dry system. When the air compressor fails, customers often go to the cheapest compressor. We then have problems with the compressor running several times a day, and problems with the noise of the compressor. Any suggestions? Douglas Hicks General Fire Equipment Co of Eastern Oregon, Inc _______________________________________________ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) Wayne Automatic Fire Sprinklers, Inc. 2006 Inductee into "The Players Hall of Fame" at The Great Games of Business Wayne Automatic Fire Sprinklers, Inc. "Best Places to Work" Rated #1 in 2006 Large Business Category by Orlando Business Journal _______________________________________________ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)